Yep.....Don’t the Generac have a disconnect breaker “under the hood” or a smaller one on the side?
So why isn’t it the disconnect?Yes there is a Circuit breaker under the hood of the generator.
Does your generator have a neutral bond? if it does you need to remove it because the ATS doesnt switch the neutral. this means running 4-wires from your generator to your ATS.The only thing exterior is the meter for utility power. (Which is located on the other side of the house about 85' away from the generator)
Actually, no the ATS will be a sub-panel to the main panel. The ATS a 100-Amp Transfer Switch w/ 16-Circuit Load Center.
I'm not sure, would it be because it could be locked under the hood? I've had to 2 electricians look at generator to wire it and only one says it needs a disconnect at the generator per NEC. So just trying to understand it.. Thanks.So why isn’t it the disconnect?
I recall reading that some of the Generac's had a disconnect external to the hood for this reason....I'm not sure, would it be because it could be locked under the hood? I've had to 2 electricians look at generator to wire it and only one says it needs a disconnect at the generator per NEC. So just trying to understand it.. Thanks.
My understanding is all Generac standby generators are floating neutral and are not bonded. There are 4 wires to be run from the generator to the ATS. I could not find any specific wording from the manual either but my understanding it that the switch is NOT bonded.Does your generator have a neutral bond? if it does you need to remove it because the ATS doesnt switch the neutral. this means running 4-wires from your generator to your ATS.
you also need to check if the ATS has a bonded neutral. If it does then you cant use it as a subpanel unless the bond can be removed. I skimmed through the manual and couldnt find any info on whether it has a bonded neutral.
it would be real easy to check. set a DVM to ohms, test from neutral bar to grnd on both the generator and ATS. shouldnt be continuityMy understanding is all Generac standby generators are floating neutral and are not bonded. There are 4 wires to be run from the generator to the ATS. I could not find any specific wording from the manual either but my understanding it that the switch is NOT bonded.
I checke the ATS and no continuity between the neutral and gound.it would be real easy to check. set a DVM to ohms, test from neutral bar to grnd on both the generator and ATS. shouldnt be continuity