Generator Service Disconnect?

mattinnc

Member
Joined
Feb 5, 2023
Messages
16
Is a service disconnect required (per NEC) where the generator is located? My ATS will be mounted inside the garage by the main panel.
I have an 11kw Generac and it does not have any external switch or breakers. Thanks!
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,096
Location
Modesto, CA
So you have no exterior disconnect to shutoff the power regardless of where its coming from?

Also the main panel will become a subpanel and the ATS will be the new main.
 
OP
M

mattinnc

Member
Joined
Feb 5, 2023
Messages
16
The only thing exterior is the meter for utility power. (Which is located on the other side of the house about 85' away from the generator)

Actually, no the ATS will be a sub-panel to the main panel. The ATS a 100-Amp Transfer Switch w/ 16-Circuit Load Center.
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,096
Location
Modesto, CA
The only thing exterior is the meter for utility power. (Which is located on the other side of the house about 85' away from the generator)

Actually, no the ATS will be a sub-panel to the main panel. The ATS a 100-Amp Transfer Switch w/ 16-Circuit Load Center.
Does your generator have a neutral bond? if it does you need to remove it because the ATS doesnt switch the neutral. this means running 4-wires from your generator to your ATS.

you also need to check if the ATS has a bonded neutral. If it does then you cant use it as a subpanel unless the bond can be removed. I skimmed through the manual and couldnt find any info on whether it has a bonded neutral.

 
OP
M

mattinnc

Member
Joined
Feb 5, 2023
Messages
16
So why isn’t it the disconnect?
I'm not sure, would it be because it could be locked under the hood? I've had to 2 electricians look at generator to wire it and only one says it needs a disconnect at the generator per NEC. So just trying to understand it.. Thanks.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,672
Location
Northern Virginia
I'm not sure, would it be because it could be locked under the hood? I've had to 2 electricians look at generator to wire it and only one says it needs a disconnect at the generator per NEC. So just trying to understand it.. Thanks.
I recall reading that some of the Generac's had a disconnect external to the hood for this reason....
 
OP
M

mattinnc

Member
Joined
Feb 5, 2023
Messages
16
Does your generator have a neutral bond? if it does you need to remove it because the ATS doesnt switch the neutral. this means running 4-wires from your generator to your ATS.

you also need to check if the ATS has a bonded neutral. If it does then you cant use it as a subpanel unless the bond can be removed. I skimmed through the manual and couldnt find any info on whether it has a bonded neutral.

My understanding is all Generac standby generators are floating neutral and are not bonded. There are 4 wires to be run from the generator to the ATS. I could not find any specific wording from the manual either but my understanding it that the switch is NOT bonded.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,096
Location
Modesto, CA
My understanding is all Generac standby generators are floating neutral and are not bonded. There are 4 wires to be run from the generator to the ATS. I could not find any specific wording from the manual either but my understanding it that the switch is NOT bonded.
it would be real easy to check. set a DVM to ohms, test from neutral bar to grnd on both the generator and ATS. shouldnt be continuity
 