Generator switch for house with two 200 amp load centers / panels

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,245
Location
Northern Virginia
If one of the legs dropped, he would have lost half the circuits in both panels plus all 240v circuits , not one whole panel. The panels are paralleled off a single feeder from the poco. To lose a panel, both hots feeding it would have to fall out of the lugs in the meter can.

My setup is the same as yours
Exactly. That's why I posted the pictures from the day job to better illustrate how the panels are paralleled.
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,516
Location
Richmond, VA
You have a typical "400A" service" as done here in Northern VA. Pictures below showing a typical "400A meter can" with SER running to the separate 200A panels (others here on the forum I believe are referring to this as a 320A meter can).

This is standard on all of our new homes here. These are pictures of a Dominion power meter can. Depending on where you are in northern VA, you might have NOVEC as your power provider but their meter cans and wiring are near identical.

You can see from the meter can lugs that the panels each get L1, L2, and ground. Dominion has not yet run the secondary to this can.

1731454871777.png1731455000037.png1731455468329.png
Are those leviton panels?
 
OP
J

joe_pinehill1

Well-known member
Joined
Feb 23, 2013
Messages
537
Location
Northern Virginia
If one of the legs dropped, he would have lost half the circuits in both panels plus all 240v circuits , not one whole panel. The panels are paralleled off a single feeder from the poco, so to lose a panel, both hots feeding it would have to fall out of the lugs in the meter can.

My setup is the same as yours
You’re probably right, I may have gotten half the story. Dominion came in the middle of the night to resplice.
 

MOS3522

Well-known member
Joined
Nov 6, 2022
Messages
1,781
Location
Colorado
Big mistake not to wire the heat into the backup panel unless that gas fireplace is automatic. Otherwise an inconvenient power outage during a winter vacation could lead to a freeze up.
 

drboom

Well-known member
Joined
Nov 16, 2014
Messages
74
We have a similar layout here - house was wired with two 200A panels each as a separate SER off the meter. We have a whole house 14kW automatic generator off a 200A ATS. I decided we'd never exceed 200A so I moved the second panel to be a subpanel off the first, limiting the house to 200A service. The second SER goes into an entrance rated disconnect that is off. This was far easier for us and resulted in a true whole house standby generator instead of picking which loads. I do have load shedding set on a few circuits as we can easily exceed the generator output if the hot tub and car charger are drawing at the same time as other high draw loads (e.g., oven).
If we ever needed to tap the second 200A feed, we'd need to run from that disconnect to a new panel and feed the circuit from there.

We've been here more than a decade and have load center monitoring on all panels and subpanels and many circuits and have never come close to 200A of draw. For our circumstances, I'd do this again the same way.

Perhaps some of you with large garages or welding facilities or other particularly large draws need more than 200A but we don't come remotely close to that.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,288
Location
Illinois near St. Louis, Missouri
It makes sense in many situations, especially when the "main" 200A panel is pretty far away from the structure. It's all about where you distribute the wire. You're basically saying "sub panels don't make sense".

There are two of us with 320A service serving 2 x 200A panels. That math is even worse. :)
I never said subpanels don't make sense. I said feeding a 200A panel from a 200A panel doesn't make much sense - especially in the case of the OP where the panels are side by side. In some cases there might be a reason to do it but in most cases the subpanel is less amperage than the feeding panel. If you have a meter main of 200A then a 200A panel seems reasonable but even in that case the meter might feed more than one panel and often the subpanels will be rated smaller than the meter.

I have a 320A service feeding 2 - 200A panels. As I understand it the derating is different on the meter base and the panels. Someone here posted the numbers and how they lined up but I don't have the reference handy.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
Our panels have separate feeds from the meter. Our neighbor also has two panels like our house. A couple months after moving in, he didn't realize he had lost power to one panel until he found the basement waste water pump wasn't working. The Utility Company had to come out, open the utility trench and resplice one of the feeds to his house.
Thats odd. Why would the utility company have to repair wiring on the load side of their meter? Thats the homeowners responsibility.
 
OP
J

joe_pinehill1

Well-known member
Joined
Feb 23, 2013
Messages
537
Location
Northern Virginia
Thats odd. Why would the utility company have to repair wiring on the load side of their meter? Thats the homeowners responsibility.
"The Utility Company had to come out, open the utility trench and resplice one of the feeds to his house." Dominion respliced the feed from the street transformer to the meter. The wire Dominion installed to the meter box failed.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
"The Utility Company had to come out, open the utility trench and resplice one of the feeds to his house." Dominion respliced the feed from the street transformer to the meter. The wire Dominion installed to the meter box failed.
Thats not what you said in your previous post.

You said one panel lost power and the 2 panels have separate feeds from the meter. So if only one panel losses power, that indicated an issue with the feed from the meter to the panel not from the transformer (or lateral splice box) to the meter.

Thats why i was confused
 

gkw4815

Member
Joined
Feb 19, 2021
Messages
11
Location
Houston, TX
I have dual 150 amp main panels tied to a 320 amp meter base. One interlocked 50 amp breaker in each panel. One 50 amp inlet with hots split to each breaker, neutral and ground tied to one of the two main panels.

Over 120 hours of running on this setup through various outages and has always worked perfectly. No issue with parallel neutral paths because there's only a single 6awg neutral wire run from the inlet to one of the panels.

Another option would be fully-independent interlocked inlets for each panel. This provides flexibility for future expansion (ie if you get a really big portable generator, like a GP17500e, two inlets would allow to to use all of its running amps instead of being limited to 50 amps).
 
To avoid these ads, REGISTER NOW!

gkw4815

Member
Joined
Feb 19, 2021
Messages
11
Location
Houston, TX
I dont think I've ever heard of dual 150's on a 320a service. Any idea why 150's were picked?
Beats me, they're original to the 1986-built house. We bought the house a few years back.

There were some other oddities with the house electrical, but most have been resolved.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,516
Location
Richmond, VA
Why so big?
I bet some of it is just to allow for the breaker spaces that are needed in newer large homes. I don't need more than 200a service, but there are more circuits than I can fit into a single panel.

Also, it just goes along with the excess that people expect in larger homes.

Three zones of hvac, a huge pool heat pump, electric range, electric dryer and still, 200a would do it, but 320a is cooler
 
OP
J

joe_pinehill1

Well-known member
Joined
Feb 23, 2013
Messages
537
Location
Northern Virginia
We have 2200 ft ranch, our model normally has one panel, but I added a 100 amp sub panel in the basement to make future work easier, so the builder used 2 panels in the garage.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,913
Location
NJ
The simplest way to avoid lots of mickey mouse **** and possible future hazards is to put an interlock in each panel with a separate 30 or 50a power inlet box for each.

Then make a splitter cord "Y" to connect from gen to one or both PIBs. The splitter cord has one plug end and 2 recept ends. They are either both 30 or both 50a. Cordage sized accordingly. Use a 4-11/16" sq box to splice or pvc j-box.

All of the permanent wiring is code compliant and only the "Y splitter cord" is custom.
 

jar944

Well-known member
Joined
Jul 26, 2010
Messages
5,917
Location
Northern VA
I bet some of it is just to allow for the breaker spaces that are needed in newer large homes. I don't need more than 200a service, but there are more circuits than I can fit into a single panel.

Also, it just goes along with the excess that people expect in larger homes.

Three zones of hvac, a huge pool heat pump, electric range, electric dryer and still, 200a would do it, but 320a is cooler

Yeah a single 200a panel isn't close to large enough for all the circuits on these (average for the area) houses. I have 200a service and a 100a sub panel and the amount of appliances rooms and areas that should be on dedicated circuits (but are not) is ridiculous and i'm gas for the stove, water heater and lower furnace. The rest of my neighbors on my street all have 320/400 and are 2-3k sqft smaller (but 100% electric).
 