I'm looking at this one over the one with the individual flip switches, this panel has two positions utility and generator power, what has me a little puzzled is on the utility side from the main panel to this sub panel if I'm right I would need to call the power company to tell them to disconnect power to the house while the work is being done because of the live wire going to the main disconnect switch?

If that's not the case I can't see how it disconnects from the utility power if still connected to the main panel but the sub panel is just acting as a switch between generator and utility.

http://www.northerntool.com/shop/tools/product_200196624_200196624
 
To avoid these ads, REGISTER NOW!

aandpdan

Well-known member
Joined
Nov 12, 2009
Messages
847
Location
In between MA and PA
The line from the meter that goes into your current panel is removed. It goes into one side of this switch. The other side goes to your generator inlet. A new line is then run from this switch into your existing panel to "feed" it.

You need to disconnect the power to install the switch. After that, it will disconnect your entire panel. You can turn both "off" if you want but only one can be on at a time.

Have you considered an interlock instead? It might be easier, and likely cheaper.
 
OP
S

subarub4

Well-known member
Joined
Feb 21, 2010
Messages
1,188
Location
Connecticut
yeah I was thinking about a interlock, my panel is a Murray so the interlock kit is $149

what I wanted to know is the generator input plug how would it be wired to the panel?

I assume I have to install another breaker but I will have to move about 4 down one slot in order for the interlock to work since the new breaker is almost at the lower part and the interlock is only but so long.
 
Last edited:

442stu

Well-known member
Joined
Nov 14, 2007
Messages
49
Check out siemens web site for the Murray interlocks. They have them for most models and they're like $30 and UL approved. Many local codes require the interlock be from the panel manufacturer and approved as such. The aftermarket kits may not be approved. YMMV, just stating my findings here in ny.
 
OP
S

subarub4

Well-known member
Joined
Feb 21, 2010
Messages
1,188
Location
Connecticut
I love this site! thanks guys! So I take it Siemens stuff interchanges with Murray panels? I can't much of any info at all on Murray stuff.

I don't think that interlock on the Lowes site will work with my panel

DSCF0106.jpg


I was thinking of buying this

http://www.interlockkit.com/murray01.htm
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
It's amazing that those interlock kits cost $150. They have to be making a profit of over $100 on each one. Unless the UL testing cost them a fortune.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
A back fed breaker is a regular breaker. It's called a back fed because the power source is coming in through that breaker in a reverse direction.
 
Last edited:

Jeff95TA

Well-known member
Joined
Aug 11, 2008
Messages
886
Location
Pittsburgh, PA
My power company wouldn't accept an interlock kit. I don't know how they'd ever find out, but I didn't chance it and did a transfer switch.
 
OP
S

subarub4

Well-known member
Joined
Feb 21, 2010
Messages
1,188
Location
Connecticut
You told them you were doing work on the panel? From what I heard a transfer panel requires a permit.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
My power company wouldn't accept an interlock kit. I don't know how they'd ever find out, but I didn't chance it and did a transfer switch.