Generators, Transfer switches and "switched neutral"

east_tn_emc

Well-known member
Joined
Aug 30, 2008
Messages
426
Location
East Tennessee
All,
I am trying to wrap my head around hooking up a generator to my house electric. I have been looking at transfer switches and the generator interlock kit so you can backfeed the panel thru a circuit breaker (it interlocks the main breaker with the generator backfeed breaker so only ONE can be closed at a given time).

There has been a lot of debate on the internet and on here about the use of the interlock kits and the neutral feed...and how transfer switches will "switch" the neutral, but the interlock kits do not switch the neutral.

I read this, and understand this to mean, that the neutral feeding back to the utility company is switched, or open, to prevent any connection between the generator, via the transfer switch, and the power company feeds. Is this correct?

I have a couple of questions...
1) why would that matter when the neutral is tied in to grounding rods at the house and at each and every pole within my utility company (as confirmed from a retired utility company lineman I know).

2) I found the wiring diagrams and install procedures for the Gentran transfer switch. If you look at the last page where you can see the wiring diagram, it looks to me like the neutral and ground from the generator inputs are tied, via bus bars, directly to the neutral and ground bus bars in the circuit breaker box. How exactly does this switch the neutral? :headscrat

I am trying to do this safely, but do not see a downside or unsafe condition possible with the interlock kit related to the neutral. Convince me otherwise.

Okay, cant attach the pdf because if size...here it is:

http://www.gen-tran.com/assets/pdfs/MTSinstall.pdf
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I use an interlock on my panel for a generator. I called my local building inspection department to verify that it would meet code and it does. The thing is that all jurisdictions may not allow an interlock device so you should call your local electrical inspector to see if you can use one.
 

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
I think because some generators have a floating neutral or maybe some codes require complete isolation perhaps for accidental back-feed reasons?

But to answer your question, the neutral doesn't have to be switched in the breaker panel.


During Hurricane Ike a few years ago, we were without power for over two weeks. Well, after a while you run out of things to do, and one of the things on the overdue to-do list was to re-wire the main breaker panel. The old panel didn't have a main, which was one major reason we wanted to swap it out.

Of course at the same time we also replaced the meter can and wiring between the can and the panel... Talk about sweating bullets hoping the power wouldn't come back on! (It was another week before they trucks even started showing up in our neighborhood!)

Long story short, at that time we put in a disconnect box that runs to the main panel. Also coming out of the disconnect is a long SO cord with a plug that goes into the 220V on our generator. So basically all we have to do it throw the main off, then throw the breaker for the disconnect, fire up the generator, and throw the disconnect and the panel gets power. I know technically you should have an Interlock kit, but since there are only two people that would be messing with the breaker panel, it's fine for our use. If we ever sell the house it's easy enough to remove the cable for the generator and then they have a plain old disconnect box for whatever use.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
You don't worry about the neutral. Just don't even think about it. Follow the installation instructions of the UL and NEC approved transfer devices or interlock kits and you'll be fine.

The neutral can be considered an extra ground for most things.

What's really confusing is the whole floating vs. tied neutral at your genset. Should you be grounding the genset to its own rod. What about when powering an RV trailer with no ground rod anywhere and rubber tires?

You can analyze these things to death if you want or you can just follow the directions.
 

aandpdan

Well-known member
Joined
Nov 12, 2009
Messages
849
Location
In between MA and PA
There has been a lot of debate on the internet and on here about the use of the interlock kits and the neutral feed...and how transfer switches will "switch" the neutral, but the interlock kits do not switch the neutral.utility company (as confirmed from a retired utility company lineman I know).

Not all transfer switches switch the neutral.
 

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
Basically if the genset has the neutral tied to the ground (EGC), switch the neutral. If the genset neutral is floating (not tied to EGC), neutral is not switched. In all cases, follow the rules of the AHJ.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
You don't worry about the neutral. Just don't even think about it. Follow the installation instructions of the UL and NEC approved transfer devices or interlock kits and you'll be fine.

The neutral can be considered an extra ground for most things.

What's really confusing is the whole floating vs. tied neutral at your genset. Should you be grounding the genset to its own rod. What about when powering an RV trailer with no ground rod anywhere and rubber tires?

You can analyze these things to death if you want or you can just follow the directions.

this is the sort of advice that gets people killed. the neutral is most certainly not an 'extra ground'
 
To avoid these ads, REGISTER NOW!

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
Well, pretend the power line got cut outside for some reason. You have your generator running but the neutral is still tied to the panel & thus to those cut lines outside. There is the ever so slight chance that someone could get a nice shock (or worse)...

However, in most systems I've seen (and as you said in your interlock setup), the neutral is not switched at all. For safety's sake make sure you have your grounds.
 

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
this is the sort of advice that gets people killed. the neutral is most certainly not an 'extra ground'

Ditto - what he said. For sure!

For the intents of this thread, why not? How about some helpful information.

The neutral is a current carrying conductor for all 120 volt circuits, and current imbalance on 240 volt circuits. The EGC is for safety, and should never carry current except in the case of a fault condition. For isolation from the POCO lines the rule about neutral switching I posted above comes into play. Another rule of thumb - If you don't know what you're doing consult a knowledgeable electrician - the life you save may be your own! Helpful enough? :D
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
The neutral is a current carrying conductor for all 120 volt circuits, and current imbalance on 240 volt circuits. The EGC is for safety, and should never carry current except in the case of a fault condition. For isolation from the POCO lines the rule about neutral switching I posted above comes into play. Another rule of thumb - If you don't know what you're doing consult a knowledgeable electrician - the life you save may be your own! Helpful enough? :D

Yes, that's much better. I'm assuming you mean ground when you say EGC. What exactly does EGC stand for?

Of course I know the neutral carries current, terminology is the problem. Been working on lots of 12 volt DC stuff in RVs lately where the ground wire carries current as well.

My genset has a floating neutral as most all portable gensets do. There is also a provided ground lug in case you want to ground the chassis I guess.
 

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
I'm assuming you mean ground when you say EGC. What exactly does EGC stand for?

My genset has a floating neutral as most all portable gensets do. There is also a provided ground lug in case you want to ground the chassis I guess.

EGC - Equipment Grounding Conductor - the proper terminology for the "third wire ground".

And no, not all gensets have a floating neutral. Otherwise transfer switches that switch the neutral would not be needed.

PS: We haven't even touched on "separately derived circuits", but I'm not opening that can of worms; not really relevant to consumer products.
 

The Frisco Kid

Well-known member
Joined
Apr 20, 2012
Messages
645
Location
Central Texas
Switching the neutral is not necessary in MOST residential applications. If you don't know what you need, consult an electrician. You need a single neutral grounding point.

Ground Fault Protection is pretty important... make sure you don't create a path that can bypass it.
 