Geothermal heat pump
asmith1923
My Barndominium is 3000 SF with 15’ ceilings. Inside I have carved out 400SF as a two story apartment. I’ve already run 1/2” pex in the floor and am ready to buy the rest of the system.
Propane was the initial plan, but the prices are outrageous. Can anyone help me design a geothermal system that I can heat DHW, heat a closed floor loop for my radiant system AND provide AC just on the apartment side? Oh, and I’m on well water.
A
asmith1923
I’m in northern Va.
3-10x10 garage doors R6
1-22x15 barn door R4
Walls R19
Ceiling R30
2” foam under floor
Heat barn to 60
Heat apartment to 68
Cool apartment to 74
It CAN BE DONE, but you are NOT going to get the design service for free ! On top of that, the installation costs will be VERY HIGH !
Geothermal heat pumps are very cost effective to run, so you will recover your money. The combination of in floor heat and A/C adds another complication. It can be done, just more installation costs.
My only advice is install wells, not horizontal tubes. With wells you can add more if required.
jack stand
Lakes Region Maine
Any intrest in burning wood?
A buddy put in geo thermal, (frederick MD) made a huge investment and I don't think that he'd do it again. I've not ask him directly as I feel it might be a "touchy" subject.
I have a barndo and the living space is a piece of cake for our mini split heat pump. Don't relate them to the thousands upon thousands of conventional ducted "heat pumps that were widely installed in new homes back in the 80's - 2000 era.
I'd consider a solar rooftop (water) collector in N VA for the shop. You'll need some storage, but solar water is a good low tech solution. The nice thing about radiant is the low temperature required, generally about 110-120.
I'd still seek out a design firm for the particulars and good results. They'll also recommend and size a hwh/boiler for any "bump up" needed in the extremes, but they'll include domestic h/w as a part of this.
A
asmith1923
I’m doing all the installation myself and have an excavator and 15 acres of woods to use.
I’m not sold on the In ground loops, but If I do they definitely be the horizontal style.
kj_mustang
Harrisonburg, VA
I priced an install and researched multiple geo heat pump brands about 7 years ago for my new house build. I decided against using them at that time. Price was twice a normal heat pump, over 60K quote for two story house, and all the brands seemed to have major repair issues and not lasting long enough to get your payback. I have propane boiler heated radiant and would do it again.
A
asmith1923
Thanks for the responses. Yeah I’ve been reading about the reliability issues, especially on well water.
Thanks kj, I was hoping someone would tell me to stick with propane. So much easier.
Thanks jack, while I have no interest in burning wood - I sure do have enough of it. The solid water is a great idea.
A
asmith1923
Dumb question but do the mini split systems offer heat in the winter? I’ll only have the heated floor on the first floor. I was think of doing a ducted system and make the first and second floors different zones. That was I could use the heat pumps upstairs in the winter.
jack stand
Lakes Region Maine
Yes they make good heat. You should gain some heat in your 2nd floor from the first floors radiant, but I have the same situation and we ran radiant tubing in the ceiling with the aluminum heat "dispersion" plates on the 2nd floor, a separate zone. Keep doing your homework, it's worth it. Research the mini splits, it's a great setup especially where you don't have the extra space for ductwork. You'll have a/c as well without all the supply and return ducts.
Firebrick43
West central Indiana
What do you mean prices o
Expand on this? Are you talking about equipment? Propane boiler and a mini split is going to be much cheaper than any Geothermal System, probably a 1/3 the cost.
Also, the best way to save money is to insulate, and your only doing R30 in the ceiling???? It should be r60. Wall should be easy to do more than r19 as well. By your picture you didn't do full foam under the floor, only the perimeter and its 1 "
toyotadriver
I don't think a ground source heat pump will pay for itself. Maybe but good chance it won't. Also, installing horizontal loops in woods will probably be a challenge. If your place was a lot bigger, I might recommend the GSHP more highly.
I'd go with propane and install a few mini splits. 400 sq ft is nothing to heat/cool with a mini split even in your climate. You could even install some mini splits in the shop area to help supplement the floor propane heat. You might end up not even using the floor heat.
Alternatively you could install mini splits and then install an outdoor wood boiler. But, instead of running it all the time like most people do, just fire it up once or twice a week and run it hard while it's running to heat the floors. Then shut it down for a few days. You will need good insulation around the water lines into the outdoor boiler if you are going to shut it down for a few days/week at a time. Your mini splits can heat during the times the boiler is shut off. But, I realize you don't want wood heat so that might be out. But, I'd at least consider it.
jack stand
Lakes Region Maine
I can't stress enough how important your insulation "package" is. I have 1 1/2" of foam outside the framing in between the wall girts, then another 1 1/2" on the inside. Each layer had all the edges sealed with (can) foam. That left room for a layer of r 13 fiberglass. There's tyvek under the metal on the outside also.
It's difficult to spend the extra money and effort on this, especially in the sweltering heat, but it's a sure bet that it's an investment with dividends every year from here on out.
4 FN 27
Minnesnowta
Wiz the only cost difference will be the heat source in this simple system. How much is a Propane Boiler vs a Geo Heat Pump and Wells? Yes there will be more cost but what is the ROI. A basic simple calculation will tell the OP which direction to go.
Adding AC does not complicate the system. It is just another source of heat and cooling with a cost difference. No more complication.
I have both Wells and Loop Field. Using directional boring you can add to a Loop Field same as a well field and the cost in our area is about the same when we did ours.
I'd be nervous about geothermal. When they don't work well, it's an expensive problem.
How about an air source heat pump with propane backup?
They don't work well because they are not designed properly. You need to find a contractor that knows what they are doing and have experience and training in Geothermal. It is 100% science. I called 8 of our Geo designers customers and they were all happy. No complaints.
All the stuff you read on the web is the ****** negative stuff. Heck I did a write up on here about how our Gas Back-up Boiler blew up. Negative. I have never done a write up about how well our Garage Door Open on the third stall performs.
We have 2 Geo System. One for the house and one for the Shop. The house has wells and the shop ground loops.
The house system is design to run down to -7° without assistance. From -8° to -1 million° there is a Natural Gas Boiler with heating coils in each of the forced air furnace/heat pumps. There is also a heat pump for the in-floor systems which also can be supplemented by the backup boiler. The Backup boiler is the main source for heating the water.
So there are 3 forced air furnace/heat pumps/AC, one for the main floor, one for the second floor, one for the bonus room above the garage in-floor heat pump (11 Zones: Anything concrete or tile has in-floor including the whole basement and upper and lower garages). Since no HVAC Contractor I have found yet can balance a house anymore I made them do the upstairs, downstairs and bonus room on 3 separate systems. The House system has 20 140 Foot vertical loops. Originally we were going to have (16) 180 foot loops but we hit fractured bedrock at 140. So we added 4 more loops to get the capacity we need. These are all water to water exchange.
Cost was about 33%+/- over conventional. At the time there was a tax rebate of 30%. Based on having a dual heat system. Geo with a natural gas back-up the house qualified for the POCO's "Back-up Relief Program". Thus any kilowatt hours the Geo systems uses is at a 50% discount.
According to the "study" based on the house and the system design Geo can save you tons of money with an initial higher investment up front. Based on 2008 (when we built) electric rates the savings over a 20 year period was estimated at $110,000.00 or $458 per month. The ROI was 4.6 years (I think, Memory again, and time the Government was offering a 30% tax credit to and that is considered in the ROI.)
Maintenance? There really isn't any other than changing filters and looking for leaks. When it gets below zero I look the system over morning and evening to make sure everything is cycling as it should.
Problems? On the house system really nothing. In the beginning the in-floor boiler would trip out showing a high pressure issue. After some head scratching and chin rubbing the tech and I sorted out that the gas boiler supplemental heat load out was routed to the heat pump load out thus the lines were reversed creating the issue. That was an installation issue...rather complex system.
Next problem. Our Triangle Tube Boiler blew up. That had nothing to do with the system.
The shop: 2 heat pumps for the in-floor and one forced air furnace/heat pump/AC. 7 Zones.
On the shop we tried the Vertical loops but hit fractured bedrock at 70 feet only 800 feet SSE of the house loop field. We ended up going with (8) 300 foot directional bored horizontal loops. This is just as effective in my area based on a high water table. We bored at and average depth of 20 feet and were in water the whole time. Water has the best thermal transfer. If you run a horizontal loop in dry sand or clay you will have problems with thermal transfer.
"A properly design system will pay for itself. My shop is 10574 sq feet. I heat office and vault, 832 sq ft feet to 68°, the car shop, machine shop, storage room, and utility room totaling 4320 sq ft to 62° and the 5422 sq ft "Cold Storage" to 50° and the highest bill this year so far with how cold it got this year was $216. Last year the highest bill was $162 with a mild winter. Air Conditioning everything except the "Cold Storage" Area is more than effective. Averaging $37.00 per month in the peak of the heat. All these costs leave out the meter rental and service charges." (quoted from another misleading GJ Thread).
OP do your research. Filter it and use caution when you seek advise or opinion on the GJ (or any web-site)...those who post a solution or opinion on every thread or most of them cannot be experts in all those fields.
Above is my shared experience with Geo...I am interested in which direction you go.
karoc
Hemphill Tx
From the 70's to the present I do HVAC work, to this day I just don't understand what the advantage is of going with geo thermal heat pumps. Heat pumps in my simple world is a pain on its own, much less adding geo to the equation. I don't think that there will be a trained HVAC person around the corner when repairs are needed. Nor will parts be that ready available, plus dealing with water that will also require some attention and finding parts for HP alone may also be problem. I think that HP's work maybe to 35* OA temp? Then again, I don't embrace systems that only few homeowners will have. If its so great why don't more homes/garage's have them? I confess, I don't know that much about geo thermal systems, but I have installed several HP's with aux heat as backup and during cold days the aux heat was on. Just saying that maybe need to look into future say 5 yrs from now.
fitter30
Peace Valley,mo
Geo has a 26% income tax credit
Need to check with your state and electric company for rebates. Geo by far is the most energy efficient system for heat or ac.
reader2580
Minneapolis, MN
I think the high initial cost of geothermal is what stops many people from using it. You also have all the horror stories of bad installations that never worked. I would like to have done geothermal for my house, but the cost was over $30,000. (The price included ductwork in the basement as the house had baseboard electric heat.) I ended up with a natural gas furnace and central A/C.
The OP is set up for in-floor radiant heat. While available in other parts of the world, I have not seen a heat pump system (air or geothermal) that will exchange the heat generated with the waster in an in-floor system. These is not difficult/complicated. All you need is a properly sized heat exchange with the refrigerant on one side and the water on the other.
Adding AC to such a system, again, is not difficult/complicated. You need a refrigerant to air air handler, standard with most mini-split systems.
I have read many horror stories about people installing geothermal with horizontal loops and not being able to extract sufficient heat from these loops. Consequently, the heat pump can not provide adequate heat to the home. Horizontal system are very large and take up a lot of land. If you don't have more land to bury a second horizontal loop, your screwed.
If I ever install a geothermal system, I would install a thermometer on the water leaving the heat pump and the water returning to the heat pump.
Too many geothermal systems are sold WITHOUT backups. You either need a LARGE generator or a secondary heat source. People can sweat through a power outage in summer without AC. I would not like to have to live through several days of no heat with ambient temps well below freezing !
Concur ! I am not smart enough to know how to calculate this. A system with both a hot water heat exchanger (for radiant in-floor heating) AND an air handler (for AC) will obviously cost more.
fitter30
Peace Valley,mo
The average ground temp in Tx 75° 10 ft down. In northern states 50° in winter and summer doesn't vary than more than 2°. In heating a geo heat pump there is no defrost and wouldnt you want to pull heat from 50° water heat exchanger or air that would be in northern states below 0° or in your case 30°. And for Ac 50° water cooled condenser or 105° air. 3 gpm design per ton through each bore hole (1 ton) with backfilling with bentonite grout. Hows seer rating 45+ and cop 5.1
pcmeiners
"Can anyone help me design a geothermal system that I can heat DHW, heat a closed floor loop for my radiant system AND provide AC just on the apartment side?"
The price for a geothermal installation is very high, but it would be particularly high per square foot for only the 400 ft area. If your going to do it, do the entire building or otherwise use an refrigerant to air unit (standard heat pump)
You could use either geothemal or an a standard air exchange heat pump with a refrigerant to water heat exchanger, for the radiant heat such as the type in the link, rated for high pressure refrigerant (type but not the size)....
Believe you could use a standard , high efficiency heat pump as the temp for the in-floor heating does not need to be that high. The only major issue is how you get air conditioning, as you would not want it through the in floor system. You would need a refrigerant valve diverting a reverse flow to a ductless air handler along with controls to do so, a good AC tech, better still an HVAC Engineer could design it. Now if you have the money you could purchase a high temperature hot water exchange heat pump system pre packaged, to do you heating, hot water an AC, but it would not be cheap ( this type heat pump is used far more outside the USA), very expensive .
A
asmith1923
Thanks everyone for your time and expertise. I have officially been talked out of geo.
I’m going to stick with propane for the floor heat. For the apartment side, I’ll need some AC. Since I only have a 7’-2” ceiling in the first floor and 7’ on the second, a ductless isn’t going to work because there’s just not enough space.
Is there a mini split ducted system that I could zone up and down stairs? I’ll need supplemental heat upstairs on the cold nights. And way more AC up than down.
fitter30
Peace Valley,mo
If you had a larger load 5+ tons.there are companies that make what you want not for such a small load. 2 ton air cooled
4 FN 27
Minnesnowta
Yep and that is all you will read...well unless you read my story. It has a happy ending (the system works as designed) but nobody publishes the stories...no issue it runs silently in the background...
Yesterday I wrote about my buddies Air Compressor explosion. I didn't write anything about how my 2 compressors here and 3 compressors at work didn't blow up.
This is why !
In some southern states ALL new government buildings MUST use geothermal !
A
asmith1923
The perimeter is 2” then a row of 1” inside that, the 6” gravel in the center. The apartment area has all 2”.
I will have 1” board and batten over tyvek on the exterior. 6” of batt insulation, vapor barrier and 3/4” plywood up 8’ then metal the rest of the way up on the inside. Ceiling will be metal as well with blown insulation. I could easily blow in r60 worth.
pcmeiners
Not understanding why no one like geothermal other than for the high inial cost. It is a heat pump with a water to air exchange, underground pipe or wells, and a water pump, nothing complicated to fix. The buried part can easily last > 100 years. which is not affected by the weather, and geothermal is approx >20% more efficient then an air to refrigerant heat pump.
Firebrick43
Because many ROI is extremely long if never. For my house, using historically high propane cost, it would take 20 plus years to have an ROI. It does seem to make since if you only have electricity available and its a very large system.
fitter30
Peace Valley,mo
Geo is just one part of the equation. The correct insulation, windows, doors and how tight the envelope is with the iaq a 1800 sq ft home $2-3 a day for heating or cooling. Build it right or pay forever the month. And no my house isn't.
pcmeiners
Fitter30.... thanks for reminding me I need to buy a load of blown insulation for my attic. It will be a most enjoyable job in the fall, as it now has 8 " of fiberglass , which I have become sensitized to over the years from working in to many damned attics. I hate fiberglass.
toyotadriver
For every happy story like yours, there's MANY unhappy stories about geothermal. Sure they are likely done by installers who don't know what they are doing....which is the problem. Too many HVAC installers are installing systems that are designed poorly and installed incorrectly. A system like that, won't work. Doesn't do much good to be preaching about the wonders of a geothermal system when many of the posters here will not be able to find a local HVAC company that knows how to do geothermal correctly.
In my case, I built a very well insulated house. I looked at geothermal extensively before deciding on a dual fuel heat pump/propane furnace. My average cooling portion of the electric bill is about $20-30 per month and the heating portion is about $20 in electricity and $20-30 in propane. It would take me forever to pay back a geothermal system.
I certainly think there is a valid time and place to use a geothermal system. For me in my area, I wouldn't consider a geothermal in a new build unless the build was at least 4000 sq ft.
Firebrick43
I completely agree, ROI will almost always be higher for insulation/other building envelope upgrades.
toyotadriver
100%. If I had to choose between a top of the line HVAC system and spend extra on insulation, I’d go the insulation route. You will get a guaranteed return on your investment improving the insulation levels. I did that on my house build 6 years ago. I calculated the return on the extra I spent on insulation to be 3 years. Everything after that first 3 years has been a bonus.
I’m always amazed to see new construction in my area and the ****** insulation levels. Build a $500k house and use code minimum insulation levels. It’s stupid.
fitter30
Peace Valley,mo
Most people don't do any homework when buying a house and are only concerned with what it looks like instead of what it has. Look at all the flipper houses in your neighborhood or tv shows cheap shoddy workmanship but the shining object keeps their attention.
reader2580
Minneapolis, MN
Most new houses are sold on floor plans and interior finishes. It is the rare home buyer who cares about what is underneath all of those interior finishes. Those varied rooflines on new houses certainly add to the curb appeal, but they don't think about the extra cost to replace the roof, but maybe they don't plan to stay long enough for a new roof.
I wanted to build a house instead of buy a pre-owned house, but the cost to build was just too high. I had a house design done for me back in 2008 that was fairly plain and only 1,200 square feet, but would have been built with high quality materials all the way through.
My current house was remodeled inside and out before I moved in. I used Smartside siding, Andersen casement windows, and other good quality materials. No builder grade vinyl windows and other **** like that. I had the back side of the ceiling in the attic covered in spray foam to stop air movement. They also fixed the blocked attic venting at the same time. I also had a new forced air system installed with new ductwork. All ductwork is metal with no flex duct.
volleyball
NY, not NYC
A lot of wild guesses so far. So good advice as well. I've been through this with my home and it has been a decade since.
You cannot design your own system on your own if you don't have experience. You will need to involve someone who know what they are doing. You can certainly fix a tooth cavity in your mouth put probably worth hiring a pro. This from a guy who has tackled just about anything on my own.
Said that I was heavily involved in my system. I chose well size, size of unit, and negotiated ductwork location and some of the registers. I carefully chose which pro to work with. Rebates required a licensed contractor.
I started with electric baseboard. I had calculated that going to gas or oil never had a positive return,ever.
But the geo system has already put me in the bank. I am saving coin until the unit fails and then it won't be a huge investment to replace the equipment.
I run the system year round. I spend less than people with any other system for a comparable house.
I agree that insulation is very important. But even up here in the north, I don't have R-50 anywhere. I found sealing to be more effective than high R numbers.
I invested more than I needed in wells as I didn't want to use aux heat more than needed. I bought a heater but have yet to install it and I've weathered many many negative degree days and nights in comfort. I knew I could not redrill the holes and I was getting 30% rebate on the holes and that kwh costs would only rise.
My home is super comfortable year round, no hot or cold spots. I could not say that with electric baseboards and a dozen thermostats.
Today I would compare against the new air heat pumps designed for cold weather. I would have to deal with outdoor units which I don't have now.
BTW my geo system does most of my DHW during the summer and supplement my winter heatings. For a 2K house
reader2580
Minneapolis, MN
How low is your electric cost if resistance electric heating is cheaper than natural gas?
My house had baseboard heat when I bought it. The electric bill was $3,500 a year per the electric company. This was with 6 cents per KWH for the heat and 12 cents per KWH for all other electricity. The only A/C was a single window unit. I spent about $23,000 to have duct work, a gas furnace, and central A/C installed. My total utility bill is almost $2,000 per year less even though I run the central A/C a lot. I figure I'll have paid off the entire HVAC install with energy savings alone in just over 10 years.