I'm learning all about solar to make a grid tied with battery back up system, and checking to see if my thinking is right on the wiring between the meter and inverter
I have a Siemens 200A combo meter Load center MC20240B1200EFC, the inverter and battery would need to be mounted about 70' aways from the meter combo panel.
For a solark 15k hybrid inverter - The line wires go from the meter to the solark, then the solark back to the combo panel main breaker. Essentially 350' of 2/0 wire and 140' of 1.5" conduit (L1,L2,N to the Solark, than L1,L2 back to the load center) I think this is called a line side tap?
If that is correct, I'm trying to compare that cost to an Enphase set up that uses a meter collar that goes behind the meter to disconnect from the grid. The wiring would be 70' of control wire to the combiner box, than 8g wire back to the load center to a 40amp breaker at the top of the bus bar.
The enphase system uses micro inverters, which could cost more than the solark single hybrid inverter, but the wire cost may offset that, plus be easier to build because i have a spare 3/4" conduit I can use coming out of the load center. The two 1.5" conduit runs will require breaking out the stucco wall to tie into the recessed load center
One other question - is the combo meter load center even rated/legal (UL, NEC etc) to add the inverter between the meter and bus bar?
Also, I'm not set on sol ark or enphase, so I'm open to other suggestions. System will be ~7-8kw
I have a Siemens 200A combo meter Load center MC20240B1200EFC, the inverter and battery would need to be mounted about 70' aways from the meter combo panel.
For a solark 15k hybrid inverter - The line wires go from the meter to the solark, then the solark back to the combo panel main breaker. Essentially 350' of 2/0 wire and 140' of 1.5" conduit (L1,L2,N to the Solark, than L1,L2 back to the load center) I think this is called a line side tap?
If that is correct, I'm trying to compare that cost to an Enphase set up that uses a meter collar that goes behind the meter to disconnect from the grid. The wiring would be 70' of control wire to the combiner box, than 8g wire back to the load center to a 40amp breaker at the top of the bus bar.
The enphase system uses micro inverters, which could cost more than the solark single hybrid inverter, but the wire cost may offset that, plus be easier to build because i have a spare 3/4" conduit I can use coming out of the load center. The two 1.5" conduit runs will require breaking out the stucco wall to tie into the recessed load center
One other question - is the combo meter load center even rated/legal (UL, NEC etc) to add the inverter between the meter and bus bar?
Also, I'm not set on sol ark or enphase, so I'm open to other suggestions. System will be ~7-8kw