GFCI Breaker tripping (New)

foamer01

Well-known member
Joined
Oct 18, 2011
Messages
245
Here goes; Just installing a new GFCI Square D home-line 20 amp single pole breaker. Read the instructions carefully. White wire in proper spot on the breaker, black wire in the proper spot on the breaker, bare ground wire to ground bar, white coiled wire attached to neutral bar and flip the breaker to on and it trips. Remove the bare ground from ground bar and holds fine. Instructions do not mentions the bare ground wire. Could someone give me some direction? Thanks Foamer
 
To avoid these ads, REGISTER NOW!

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
Here goes; Just installing a new GFCI Square D home-line 20 amp single pole breaker. Read the instructions carefully. White wire in proper spot on the breaker, black wire in the proper spot on the breaker, bare ground wire to ground bar, white coiled wire attached to neutral bar and flip the breaker to on and it trips. Remove the bare ground from ground bar and holds fine. Instructions do not mentions the bare ground wire. Could someone give me some direction? Thanks Foamer



Sounds to me like the ground and neutral are bonded together somewhere in that circuit.

Is this a new circuit you ran or are you converting an existing circuit?
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,755
All it takes is the grounding conductor to contact the grounded (neutral) conductor, won't trip a breaker but will play havoc with a GFCI. Check every box or device on the circuit.
 
OP
F

foamer01

Well-known member
Joined
Oct 18, 2011
Messages
245
This is a new circuit, direct bury out to a pool. Seems to be pretty straight forward. So just so I am clear, I should be able to attach the bare ground to the ground bar and have this work properly? Or am I suppose to attach the bare wire to the ground bar? Thanks.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
Not sure why your GFCI breaker has a bare ground wire. I just installed two GFCI breakers in my Siemens panel, type QP breakers, and there was no bare ground wire. Just a hot lead, neutral in and neutral out.

GFCIs don't look for stray current on the bare ground lead, they only look to see if current through the neutral is equal to current through the hot lead. Just don't see where bare or green ground comes into play.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,016
Location
Modesto, CA
To everyone confused about the bare/ground wire, I think te OP is referring to the EGC for the circuit.

Sounds to me like the ground and neutral are bonded together somewhere in that circuit.

Is this a new circuit you ran or are you converting an existing circuit?

All it takes is the grounding conductor to contact the grounded (neutral) conductor, won't trip a breaker but will play havoc with a GFCI. Check every box or device on the circuit.

Agreed!! +1 Sounds like current is flowing on an alternate path via the ground wire since the breaker doesnt trip with the ground wire removed from the buss!!
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
I was confused. I thought the OP was suggesting there was an ECG, bare ground wire coming out of the new GFCI breaker.

It does sound like the breaker is installed correctly. Remove any loads from the circuit, remove circuit wires from panel. Measure resistance from ground bare wire to neutral, should be open. Agree with others, you have a ground to neutral short somewhere in the circuit.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
This is a new circuit, direct bury out to a pool. Seems to be pretty straight forward. So just so I am clear, I should be able to attach the bare ground to the ground bar and have this work properly? Or am I suppose to attach the bare wire to the ground bar? Thanks.

Bare wire to the ground bar. What are you using to make the run,pvc or uf wire. What outlet are you using,and is the pump plugged in when the gfi trips. Did you open the outlet up and pull everything out and then try the breaker. You may just have a nick in the wire hitting the side of box
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
Uh what? Only your black wire should be attached to the breaker, white goes to neutral bar.

not on a gfci breaker. the breaker will have an additional lug for the neutral of that circuit to land to and a white pig tail that goes to the neutral bar.
 
OP
F

foamer01

Well-known member
Joined
Oct 18, 2011
Messages
245
Here are a couple of pictures that I took quick. Please don't judge me by my messy box. There is no equipment hooked up to the outlet. Thanks
 

Attachments

  • IMG_8452.jpg
    IMG_8452.jpg
    145.4 KB · Views: 75
  • IMG_8448.jpg
    IMG_8448.jpg
    139.4 KB · Views: 56
  • IMG_8449.jpg
    IMG_8449.jpg
    134.2 KB · Views: 55
  • IMG_8450.jpg
    IMG_8450.jpg
    137.7 KB · Views: 70
  • IMG_8447.jpg
    IMG_8447.jpg
    148.4 KB · Views: 71
  • IMG_8445.jpg
    IMG_8445.jpg
    133.1 KB · Views: 57
To avoid these ads, REGISTER NOW!

Duck tape Bill

Well-known member
Joined
Jul 6, 2012
Messages
293
Location
Maryland
Is that a GFCI outlet? Why do you have both a GFCI outlet & breaker? And why is there electrical tape wrapped around the neutral wire in the box just above the sheathing? if you cut into the neutral wire maybe that's the problem?
 

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
Nice pics. Could your receptacle be wired on the load side? Looks like you have enough UF to pull up and wirenut that neutral if it's nicked.

You required to have both a gfci breaker and recep?
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Yeah no point in having a gfi outlet and breaker, but in the gfi outlet box check to see if the ground wire is against the neutral when you pushed the outlet in which is common
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
Are there other gfi devices fed from this panel that are operating properly? I see no other gfi breakers, but are there gfi outlets working properly?

Is this a main or sub panel?

As others have pointed out, gfi breaker OR gfi outlet. Not both!
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
I don't want to sound like my kid and no disrespect to you, but why? Trust me I am no electrician just wanting to learn. Thanks

because you have it protected at the source, no need to protect it at the point of use. Also since the GFCI receptacle monitors between the neutral and ground, that can cause upstream GFCI's to trip. try this and report back. also make sure that the ground and neutral are not touching in the outlet box.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You don't need both the GFCI breaker and outlet, but if the cable is buried shallow at 12" or so, then the GFCI breaker is required for protecting the circuit from the source. This applies to buried 120V, 20A or less circuits. See NEC 300.5. It's best to keep the breaker and dump the outlet.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Also since the GFCI receptacle monitors between the neutral and ground, that can cause upstream GFCI's to trip. try this and report back. also make sure that the ground and neutral are not touching in the outlet box.
Monitors between the ungrounded conductor and the grounded one.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,755
There's no need to have both a GFCI receptacle & breaker; http://www.garagejournal.com/forum/showthread.php?p=401096&mode=linear#post401096

Replace the receptacle (check the wiring there since it's the only thing we can't see in the pictures) with a normal 20A.... at least that's what I would do.

Why spend the extra $ for a 20A? If a 20A attachment plug is required the circuit would need to be dedicated, 15A is fine, while not germane to this discussion a 15A is rated for 20A feed through to other receptacles.
 
OP
F

foamer01

Well-known member
Joined
Oct 18, 2011
Messages
245
Update: Ground and Neutral were not touching in the box. Taking the advice, I removed the GFCI outlet and replaced it with a regular 20amp outlet. With the bare ground once again in the ground bar it is holding and tested just fine. Coming from a layman it just seemed like two safety's (breaker & GFCI) were better than one, though in this case I guess not. Thank you very much for taking time to read the post and advise. Foamer
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,016
Location
Modesto, CA
because you have it protected at the source, no need to protect it at the point of use. Also since the GFCI receptacle monitors between the neutral and ground, that can cause upstream GFCI's to trip. try this and report back. also make sure that the ground and neutral are not touching in the outlet box.

No a GFCI monitors current flow between the hot and neutral conductor.

Update: Ground and Neutral were not touching in the box. Taking the advice, I removed the GFCI outlet and replaced it with a regular 20amp outlet. With the bare ground once again in the ground bar it is holding and tested just fine. Coming from a layman it just seemed like two safety's (breaker & GFCI) were better than one, though in this case I guess not. Thank you very much for taking time to read the post and advise. Foamer

The point is, 2 GFCIs on the same circuit are redundant and is a waste of money. Plus, as u have learned, they can cause issues such as nuissance trips. What extra safety do u think your gaining by having 2 GFCIs? The response time isnt increased....what else could u gain? I think if u knew how they functioned, then u would understand why 2 GFCIs arent better than 1....
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
No a GFCI monitors current flow between the hot and neutral conductor.



The point is, 2 GFCIs on the same circuit are redundant and is a waste of money. Plus, as u have learned, they can cause issues such as nuissance trips. What extra safety do u think your gaining by having 2 GFCIs? The response time isnt increased....what else could u gain? I think if u knew how they functioned, then u would understand why 2 GFCIs arent better than 1....

yea I realized I worded it wrong.
 