To avoid these ads, REGISTER NOW!

gfci causing bad breaker?

mtnwalton

Well-known member
Joined
Apr 25, 2010
Messages
210
Need some help; i've searched, but haven't read every response to every thread. if this has been covered, sorry.

We're doing a little bath remodel, new vanity and top etc. There was one outlet by the vanity before, not GFCI. I'm replacing that with Gfci outlet, and adding two other outlets. Everything looked good and I was finishing up until I plugged in my shop vac to cleanup. Maybe a bad idea. gfci tripped, won't reset. I removed it and now the feed wire is dead.

Can a GFCI tripping make a breaker go bad??. Thanks for any help.
 
To avoid these ads, REGISTER NOW!

Tim The Tool Man

Well-known member
Joined
Mar 1, 2012
Messages
1,520
Location
Lehigh Valley, PA
No. Sounds like you inadvertently loosened a wire during your remodel. Maybe on another outlet from an adjoining room. You might have pulled on wire a bit to hard when you were working on it.

I would pull all the outlets and check the wiring. Also disconnect the slave outlets and see if that narrows the problem down any.
 
OP
M

mtnwalton

Well-known member
Joined
Apr 25, 2010
Messages
210
I didn't disturb the wires that led to the outlet and didn't touch any wires from other sources. I checked the slave outlets, everything was good until the vac tripped the gfci. I'm stumped
 

frankush

Well-known member
Joined
Oct 23, 2011
Messages
1,156
Location
IL
Sometimes when breakers trip, they won't reset. If the breaker won't reset, replace it. Install a new breaker and check to see if you have 120V, without reinstalling the GFI. You will occasionally get a brand new GFI that's bad. GFI's generally won't reset until they have power supplied to them. A breaker that trips immediately, is trying to reset but a fault condition still exists.
 
Last edited:

RECox286

Well-known member
Joined
Apr 11, 2012
Messages
1,399
Location
South Joisey (yeah, that is part of the USA)
If I get this right, the circuit breaker tripped, and now you have no

power to the (no matter which type) receptacle. Sounds like you

inadvertently caused a short in the wiring somewhere while you had

things apart, which became apparent when you "plugged in the

vacuum". Perhaps the neutral or ground wire touched the hot wire

because of the tuck. Sometimes it doesn't take a lot of movement

to do this if you aren't careful how you install the equipment.

If you are trying to reset the c/b, some brands must be turned to

full OFF before they will stay ON. Try that. If the c/b immediately

snaps to TRIP position then you should disassemble the construction

to check and see if you wired everything correctly; feed hot wire to

LINE/gold screw, feed neutral to LINE/silver screw, continuation hot wire

to LOAD/gold screw, continuation neutral to LOAD/silver screw, all grounds

bonded and to the ground screw. Everything tucked so that no bare

wires will touch what they shouldn't. Then set the c/b and see if it

holds. Go to the receptacles and test each one for operation, including

test button on GFI, and reset. Then hopefully everything should work.

Uncle Bob
 
To avoid these ads, REGISTER NOW!
OP
M

mtnwalton

Well-known member
Joined
Apr 25, 2010
Messages
210
Thanks for the replies. Right now there are no receps; only bare wires. I reset the breaker (after full off as usual) and it feels normal. I may have a breaker that was going bad anyway. I've read since that that can happen. Tomorrow i'll get a new breaker, install and then check the wires again. I just hope to be able to use the GFCI again.

I have also learned NOT to use a gfic for motors, at least not the type i have.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Did you try turning breaker all the way off before resetting it?
If breaker is tripped in center position it needs to be kicked all the way over before resetting it:shocking:
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
>I have also learned NOT to use a gfic for motors, at least not the type i have.

I have a lot of motors around here including Cheep China that are used with GFCIs and no problems. What kind of motors do you have?
 
OP
M

mtnwalton

Well-known member
Joined
Apr 25, 2010
Messages
210
problem solved and now I feel really dumb. There was another gfci across the house that was tripped. Not the normal install but I should have thought of it. Thanks to all for your patience and help.
 
To avoid these ads, REGISTER NOW!