I got a puzzler. Bought a house with a federal Pacific load panel. Seller had to change the service out which really frosted him up. He was not happy with that expense.
The load center is inside the house with the exception of a sub panel outside the house, next to the meter. This supplies the pool circuit with 220 for the pumps.
Next to the pumps is a smaller panel with a 220 breaker for the pumps, and a 125v GFCI for the pool light.
Pool light burns out. I check the timer using my trusty Navy Wiggins, find power, so check the GFCI. It's on.
Ok, burned out bulb. I then test the GFCI and it does not trip. Hmmm. Maybe a coincidence with the bulb. Try a new GFCI with same result. Can be manually tripped, but won't test. Ground the GFCI neutral and the breaker trips
I'm now thinking when the service was changed they mucked something up. Any ideas where to look? Pool panel is CH breaker with the metal hooks on top.
The load center is inside the house with the exception of a sub panel outside the house, next to the meter. This supplies the pool circuit with 220 for the pumps.
Next to the pumps is a smaller panel with a 220 breaker for the pumps, and a 125v GFCI for the pool light.
Pool light burns out. I check the timer using my trusty Navy Wiggins, find power, so check the GFCI. It's on.
Ok, burned out bulb. I then test the GFCI and it does not trip. Hmmm. Maybe a coincidence with the bulb. Try a new GFCI with same result. Can be manually tripped, but won't test. Ground the GFCI neutral and the breaker trips
I'm now thinking when the service was changed they mucked something up. Any ideas where to look? Pool panel is CH breaker with the metal hooks on top.