GFCI issue with hot tub

fourjeepin

Well-known member
Joined
Feb 12, 2011
Messages
3,679
Location
Atlanta, GA
GFCI immediately trips when I flip it from off to on. What is the best way to diagnose the issue?

GFCI is new, as is the control box it is connected to. Tub came with my house and I am finally trying to get it working. The heater was broken so I replaced it with a controller and put in the GFCI.

Here’s a picture of the sub panel. Panel was prexisting. The other two 240 breakers are not connected as they are no longer needed with the new spa controller.
 

Attachments

  • image.jpg
    image.jpg
    82.6 KB · Views: 80
To avoid these ads, REGISTER NOW!

38 Dodge Coupe

ALLIANCE MEMBER
Joined
Mar 19, 2013
Messages
421
Location
Delaware Ohio
Just experienced this on my cal spa. In my case the heater element shorted and trips breaker. I ordered replacement heater element and that took care of it.


Sent from my iPad using Garage Journal
 
OP
F

fourjeepin

Well-known member
Joined
Feb 12, 2011
Messages
3,679
Location
Atlanta, GA
Electrical issue is resolved thanks to you guys. Now to address the two leaking joints. After replacing most of the pipes, I feared there would be leaks.

Tub is in an attached sunroom. All plumbing runs thru the interior wall into a basement closet. I had to replumb most everything in that closet.
 

Attachments

  • 09678C5C-FEDE-4C09-B048-2A495A143AF1.jpg
    09678C5C-FEDE-4C09-B048-2A495A143AF1.jpg
    146.4 KB · Views: 42
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,876
Location
NW Iowa
This would be because it’s also an arc fault right?

No it's just a GFCI. It measures current on all the wires and if all the current doesn't go back though the breaker it will trip. The OP's neutral going straight to the buss allowed current to bypass the breaker.
 

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
No it's just a GFCI. It measures current on all the wires and if all the current doesn't go back though the breaker it will trip. The OP's neutral going straight to the buss allowed current to bypass the breaker.



So what would the curly wire from the breaker going to the neutral be for?

Just never seen a gfci like this. Our arc faults have the neutral pigtail.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,876
Location
NW Iowa
So what would the curly wire from the breaker going to the neutral be for?

Just never seen a gfci like this. Our arc faults have the neutral pigtail.

Not exactly sure of the question.

There is three lugs on the breaker, (2) hots and a neutral. The hots go though the breaker and connect to the buss. The neutral goes though the breaker so it can measure current and then connects to the neutral bus though the curly wire.

Fun fact, AFCI's will also trip on current imbalance just like a GFCI. I think afci's will trip somewhere around 30mA imbalance vs. a GFCI that trips with 4-6mA imbalance.
 
Last edited:

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,758
Location
Long Island
So what would the curly wire from the breaker going to the neutral be for?

Just never seen a gfci like this. Our arc faults have the neutral pigtail.

Bert spelled it out. The neutral from the circuit hooks up to the breaker. The curly wire connects to the panel neutral bus, giving the neutral on the circuit a path back there.

AFCI breakers need a neutral in order to draw power to run their circuitry.
 
OP
F

fourjeepin

Well-known member
Joined
Feb 12, 2011
Messages
3,679
Location
Atlanta, GA
Tub is pumping water! Had one joint that I neglected to glue and one union that wasn’t fully seated. I haven’t tried high speed to build any pressure yet. Still filling with water and watching for other leaks. Tub has been sitting for at least 8 years since I bought this house so it will need a bit of cleaning before it’s first use. I did drop a few chlorine tablets in it, but almost zero circulation.
 

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
Bert spelled it out. The neutral from the circuit hooks up to the breaker. The curly wire connects to the panel neutral bus, giving the neutral on the circuit a path back there.



AFCI breakers need a neutral in order to draw power to run their circuitry.



Ya I knew why they were on afci but didn’t realize gfci breakers had them as well.

Thanks for the info.
 