To avoid these ads, REGISTER NOW!

GFCI load side not working

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
26,208
Location
Niagara Region, Ontario, Canada
new GFCI at a laundry sink, a 24" LED ballast by-pass converted florescent fixture with a pull chain switch over the sink attached to the load side of the GFCI . worked last week when it was all installed, now it's dead. no power coming from the GFCI , the receptacle works, not the load side. must be defective. anything else it can be?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
The GFCI receptacle works but the load side terminals do not?

how are you testing it?

The tangs in the receptacle are connected to the load side terminals
 
OP
T

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
26,208
Location
Niagara Region, Ontario, Canada
receptacle works but the load side is dead . first tried another bulb, same results.
then tested for voltage at the fixture ( before & after the switch), nothing . then thought a bad connection at the GFI, there's no voltage at the load terminals .
when the electrician was there and first tried the light after wiring it all up, it didn't come on. twisted the bulb & it came on. it hasn't been used since, until today when I was going to show someone .
 
To avoid these ads, REGISTER NOW!

Yankeefarmer

Well-known member
Joined
Jul 25, 2011
Messages
1,225
Location
Connecticut
I had to replace a GFCI receptacle at my daughter’s house that failed that way. Receptacle worked ok, no power at the load terminals feeding downstream devices.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,133
Location
Central Iowa
I've seen that exact scenario quite a few times. I've never researched why or how that happens because I just don't care. Replace the receptacle and all will be well.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
20,274
Location
Northern Virginia
Oddly I have a Leviton gfi that the outlet itself does not work, yet all the outlets connected on the load side work and the gfi trips when tested from them.

Low on my priority to swap out.
 
To avoid these ads, REGISTER NOW!
Top Bottom