Hey guys,
The shop is moving along well. the roof started going on yesterday, and we should be done with the shell by next week. Then i will take over with the inside.


My question is, in a garage or workshop, will i need to install GFCI outlets everywhere or just around a sink if I have one. I am going by what ever version of the NEC that Florida uses. My initial wiring will be pretty minimal, just a fraction of the outlets, and some of the lights.

Tom
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,042
Location
Minneapolis
From what I can find online Florida has adopted the 2008 edition of the NEC, which means you need GFCI protection on all receptacles in the garage. For future reference it's covered in Article 210.8(A)2.
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
I belive if you feed the outlets downline from a GFI used as the first outlet from the panel it will protect the whole circuit.
 
OP
T

Tscott

Well-known member
Joined
Oct 17, 2006
Messages
1,484
Location
Keystone Heights, FL.
From what I can find online Florida has adopted the 2008 edition of the NEC, which means you need GFCI protection on all receptacles in the garage. For future reference it's covered in Article 210.8(A)2.


Thanks guys,
For everyones general info. I found that you can view versions of the NEC code at the below link:

http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=70

More specifically the 2008 version can be viewed here:

http://www.nfpa.org/freecodes/free_access_document.asp?id=7008SB



There is of course no copy or paste, but at least you can read it without shelling out the 75 bucks to get a hard copy or PDF.

I will plan to use GFCI breakers for the outlets.

Tom
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,042
Location
Minneapolis
I belive if you feed the outlets downline from a GFI used as the first outlet from the panel it will protect the whole circuit.

Yes. I think you could also use GFI breakers instead?

You can do it either way. More often than not people will use the feedthrough feature on a GFCI receptacle since it's less expensive than buying GFCI circuit breakers.
 
To avoid these ads, REGISTER NOW!

pereiracycles

Member
Joined
Sep 24, 2009
Messages
16
Hope you guys don't mind me reviving this dead thread. From the code it sounds like the GFCI receptacles are required for all garage outlets. Can they or can't they be wired with GFCI breakers or downstream of GFCI receptacles? I'd rather not shell out for 12 GFCIs if I don't have to.
 

ghnl

Well-known member
Joined
Mar 27, 2009
Messages
1,372
Location
Mebane, NC
Either a GFI circuit breaker -or- a GFI outlet as the first outlet in the circuit then feed the remaining outlets from that GFI outlet using the 'feed' terminals. i.e. ALL the outlets need to be protected - but they don't all need to be GFI outlets (because if wired as described, all outlets are GFI protected).

GFI outlets usually come with a page of stickers you can apply to the downstream outlets to indicate they are properly protected.
 

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
Does your garage have to be inspected? If not, I would put regular outlets.

I can see the point for them in the bathroom or kitchen, but in the garage... when was the last time you had a pool of standing water in there and accidentally dropped your curling iron in it? :lol_hitti

They seem like a good idea, but they are a very finicky with high load applications like power tools, 120v air compressors, etc. Also they don't get along with block heaters very well either.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
You need GFCI protection to meet code, on the ground floor. How you accomplish this, is up to you.

1) GFCI circuit breakers in the panel for each receptacle circuit, kinda pricey but works well and the breakers are probably not as prone to failure as the much cheaper GFCI receptacles. You use standard duplex receptacles in the boxes.

2) install a GFCI receptacle at the beginning of each circuit and supply all other boxes (with standard receptacles in them) from the feed thru of the GFCI.

3) install a GFCI receptacle in every position in every box. Again, rather pricey.

Charles
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I put them in my shop, code or no code. Tools are double insulated, I'm careful with spills - still, stuff happens. I put one at the head of each plug run to protect the downstream outlets.
 

pereiracycles

Member
Joined
Sep 24, 2009
Messages
16
I plan to get the work permitted and inspected, so I want to do it right. Thanks for the info. Much clearer now.
 