One of the emails from the AHJ was in my spam for some reason... It noted that the city is under IRC 2012 and included a quote from that.
Code:
E3902.2 Garage and Accessory Building Receptacles
125-volt, single-phase, 15- or 20-ampere receptacles installed in garages and grade-level portions of unfinished accessory buildings used for storage or work areas shall have ground-fault circuit-interrupter protection for personnel. [210.8(A)(2)]
E3902.3 Outdoor Receptacles
125-volt, single-phase, 15- and 20-ampere receptacles installed outdoors shall have ground-fault circuit-interrupter protection for personnel. [210.8(A)(3)]
They go on to say:
Code:
ALL receptacles MUST have GFCI protection. The lights DO NOT.
I thought IRC only covered mechanical construction details and was surprised it included electric.
So he apparently isn't totally accurate about ALL receptacles as it is only 120 V not 240V. And rather than say lights don't need it I think it would be more accurate to say hardwired devices don't need it. If lights are plugged into receptacles I expect they need GFCI.
I think the guy is getting tired of my questions. I plan to proceed to just do GFCI on the 120V receptacles and deal with any issues at inspection.
Will use GFCI breakers for high ones like the jackshaft openers.