GFCI trips instantly

Stepper

Active member
Joined
Mar 12, 2012
Messages
30
Location
Michigan, N of AA
I have an older rental property that only has 2 wire infrastructure throughout the house. The rental inspection required that I replace all 3-hole outlets with 2-hole receptacles. In addition, I had to replace a standard outlet by the kitchen sink with a gfci outlet. I correctly installed the white/neutral and the black/hot to the correct terminals. Best I can tell, I have the line vs. load wires hooked-up correctly.
My problem has to do with the fact that the instant I restore power to the outlet, it instantly trips and cannot be reset. The is now ground wire available to use, as the wiring does not have it and the receptacle box itself is not grounded.

I checked the single outlet downstream of the gfci and it seems to be fine...I.e. no cross wiring or exposed wires.

Any ideas how to troubleshoot this.
 
To avoid these ads, REGISTER NOW!

Ch3No2

Well-known member
Joined
Nov 27, 2009
Messages
356
Re: Gfci trips instantly

You can't "share" neutral wires when using a GFCI
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Re: Gfci trips instantly

First, u should remove the wires from the load terminal and reset the GFCI to see if it holds. If it does, then u obviously know the problem is downstream. If it wont hold or reset u should make sure u have the correct wires on the correct terminals, ie. line wires on line terminal, hot on hot and neutral on neutral terminals. Another possibility, IF the wiring is good, is the GFCI is bad out of the box. This is pretty rare but could happen! Try using another NEW GFCI and see what happens.
 
Last edited:
OP
S

Stepper

Active member
Joined
Mar 12, 2012
Messages
30
Location
Michigan, N of AA
Re: Gfci trips instantly

Can you elaborate on what you mean by "share" the neutral? Currently a neutral wire is attached to the line screw and another separate neutral is attached to the load screw on the receptacle.
 

Ch3No2

Well-known member
Joined
Nov 27, 2009
Messages
356
Re: Gfci trips instantly

The GFCI requires a dedicated Neutral before being branched to other rcepticles
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Re: Gfci trips instantly

Disconnect the downstream wires from the load connections, then turn on power. If it still trips, then reverse the black and white wires at the GFCI, and try it, it if works OK, you probably have crossed wires at the panel or somewhere in between. This is an older house, so anything is possible. You do need to label this outlet as NO GROUND also.

Charles
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
Re: Gfci trips instantly

Gfi's monitor the current going into the device and also coming back on the neutral. If the currents don't match then the electronics shut it off. The shared neutral refers to another connection that allows the current to return to the fuse box via another wire. Then incoming current doesn't match and it kills the circuit in 1/40 th of a second. I agree with disconnecting down stream devices and see what happens. If it works then check the down stream devices for a "shared" neutral.
 
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Re: Gfci trips instantly

Disconnect the downstream wires from the load connections, then turn on power. If it still trips, then reverse the black and white wires at the GFCI, and try it, it if works OK, you probably have crossed wires at the panel or somewhere in between. This is an older house, so anything is possible. You do need to label this outlet as NO GROUND also.

Charles

Gfi's monitor the current going into the device and also coming back on the neutral. If the currents don't match then the electronics shut it off. The shared neutral refers to another connection that allows the current to return to the fuse box via another wire. Then incoming current doesn't match and it kills the circuit in 1/40 th of a second. I agree with disconnecting down stream devices and see what happens. If it works then check the down stream devices for a "shared" neutral.

Both are correct....in other words....that neutral on the output could have a parallel connection somewhere to another neutral going back to your meter.

So, if you as charles says....disconnect the load side....if the GFIC does not trip....then your load side has an issue.
 

VHF

Well-known member
Joined
Oct 27, 2008
Messages
420
Location
NW Wisconsin
Re: Gfci trips instantly

If the GFCI recepticle does reset with nothing connected to the load side, a shared neutral on the downstream circuit is likeley. Just hook it up with pigtails so only that recepticle is GFCI protected (i.e. nothing connected to load terminals.) Biggest challenege might be fitting everything back in the box with a couple wire nuts, pigtails, and the GFCI recepticle itself!

As already mentioned, make sure it is labeled "No Equipment Ground" in a 2-wire installation. The GFCI functionality will still work fine as that does not rely on the ground.
 
OP
S

Stepper

Active member
Joined
Mar 12, 2012
Messages
30
Location
Michigan, N of AA
Re: Gfci trips instantly

By pig tailing the wires and having them attach only to the line side terminals, I was able to keep it from tripping. Thanks for the advice.
 

1tonstroke

Member
Joined
Feb 6, 2010
Messages
9
Re: Gfci trips instantly

If there are any fluorescent lights on the circuit they have been known to trip GFCI's due to leakage.
 