I have had them fail and I have one that hasn't had the test button hit in a while but I was out in the wet and got a tingle, I would have thought it would trip. Do they fail in this regard?
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Older ones are more prone to this. I don't know the year, but the specs changed dramatically at one point for GFCI's and the early ones are much more likely to to either jam or not work. Now if the electronics inside fail or get zapped by a surge they trip open. Hubbell has one that does a self test of the circuitry every minute, along with having a failure and power lights. It can also be manually tested. I'll bet its expensive.

The GFCI that Tests Itself!

Edit: if you have one that will work if the hot and neutral are reversed, you have one of the older type. When the hot and neutral are reversed, the receptacle will work normally but has no GF protection. The changes in the rules required that if H/N are reversed, then the contacts in the device cannot close and will stay tripped. There is also a warning light on these.

Charles
 
Last edited:

Alan Douglas

Well-known member
Joined
Jun 4, 2011
Messages
295
Location
Cape Cod, Mass.
You might have enough leakage current to feel, but not enough to trip the GFCI. I believe the trip point was 6 milliamps (no idea if it still is). You can definitely feel that.
 

lbmcse

Active member
Joined
Apr 22, 2013
Messages
30
You might have enough leakage current to feel, but not enough to trip the GFCI. I believe the trip point was 6 milliamps (no idea if it still is). You can definitely feel that.

4-6 mA is correct. I can't imagine a scenario where one could feel a tingle, but it wouldn't trip the GFCI.

I've never heard of a GFCI failing to work, but that's probably my ignorance. Sounds like you have a bad one. I'd replace it immediately if it were me.
 
To avoid these ads, REGISTER NOW!

troyks

Member
Joined
Aug 27, 2014
Messages
23
Location
Kansas
The threshold of human perception of a shock is only around 1 mA, so there are instances where a GFCI could be working fine that you could still feel a tingling sensation. 6-10 mA is the point where a shock starts becoming painful, and is above where a standard residential GFCI should trip.
 