Go from 40amp breaker to 50amp?

Andy_GTS

Well-known member
Joined
Jan 12, 2017
Messages
81
Location
Racine, WI
I have a detached garage with a subpanel. I have 100amp service to my house with a 40amp breaker and 8-3 wire to the subpanel. The run is approximately 65ft. As I am adding additional circuits to the garage, I'm considering replacing the 40 amp breaker with a 50amp. Is this feasible, recommended, or even legal?
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,766
Location
NW Iowa
If it is NM cable (aka romex) you are limited to 40A.
It sounds like that is what you have since you say 8-3. I am assuming it is copper as well.
 
OP
A

Andy_GTS

Well-known member
Joined
Jan 12, 2017
Messages
81
Location
Racine, WI
IMG_0254_zpsygnlec77.jpg

IMG_0249_zpsaluu2sgh.jpg


Not great pictures, I know. Copper. THHN is printed on it. The sheathing says NM-B.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,066
Location
Modesto, CA
I have a detached garage with a subpanel. I have 100amp service to my house with a 40amp breaker and 8-3 wire to the subpanel. The run is approximately 65ft. As I am adding additional circuits to the garage, I'm considering replacing the 40 amp breaker with a 50amp. Is this feasible, recommended, or even legal?

8/3 NM-b is limited to 40a...

But NM-b is not permitted in wet locations which includes underground conduits.

Does this cable run underground?

IMG_0254_zpsygnlec77.jpg

IMG_0249_zpsaluu2sgh.jpg


Not great pictures, I know. Copper. THHN is printed on it. The sheathing says NM-B.

Thats strange. NM-b doesnt have individually labeled conductors.

Do those black and red wires come from the NM-b cable?
 
OP
A

Andy_GTS

Well-known member
Joined
Jan 12, 2017
Messages
81
Location
Racine, WI
8/3 NM-b is limited to 40a...

But NM-b is not permitted in wet locations which includes underground conduits.

Does this cable run underground?



Thats strange. NM-b doesnt have individually labeled conductors.

Do those black and red wires come from the NM-b cable?

The NM-b runs from the house panel to a junction box by the riser. It is connected to wires labeled THHN I believe. Those run about 60ft underground in PVC conduit maybe a foot deep or so.
 
OP
A

Andy_GTS

Well-known member
Joined
Jan 12, 2017
Messages
81
Location
Racine, WI
So you're saying the subpanel in the detached garage is full? What's on it? And what else are you planning to add?

The subpanel has:
50 amp main
15 amp 110v (lights)
20 amp 110v (outlets)
20 amp 220v (compressor)
30 amp 220v (welder/lift)

Not looking to add anymore than that. Maybe I should remove some if 40 amps isn't enough???
 
To avoid these ads, REGISTER NOW!

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
I would just leave it, also, unless it is tripping.

Upgrading would mean new wire. If perchance the THWN is #6, then you could just replace the NM-B and get to 60A, but otherwise you'd be replacing everything (and it looks smaller than #6 to me). If the conduit is 3/4", you can keep it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,066
Location
Modesto, CA
The NM-b runs from the house panel to a junction box by the riser. It is connected to wires labeled THHN I believe. Those run about 60ft underground in PVC conduit maybe a foot deep or so.

ok that makes more sense.

What gauge is the THWN??

The subpanel has:
50 amp main
15 amp 110v (lights)
20 amp 110v (outlets)
20 amp 220v (compressor)
30 amp 220v (welder/lift)

Not looking to add anymore than that. Maybe I should remove some if 40 amps isn't enough???

Whats the most u run at the same time?
 
OP
A

Andy_GTS

Well-known member
Joined
Jan 12, 2017
Messages
81
Location
Racine, WI
It's all 8 gauge from what I can tell. The most I can imaging using is raising the lift and having the conpressor start at the same time. The lift is 23amps and the compressor is 17.5amps. And then whatever the lights are. This would be unlikely but the most possible I would think.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,066
Location
Modesto, CA
It's all 8 gauge from what I can tell. The most I can imaging using is raising the lift and having the conpressor start at the same time. The lift is 23amps and the compressor is 17.5amps. And then whatever the lights are. This would be unlikely but the most possible I would think.

Well if u want 10 extra amps, u would need to replace the 8/3 NM-b with 6/3 NM-b or #8 THWN in pipe which is rated for 50a...
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
It's all 8 gauge from what I can tell. The most I can imaging using is raising the lift and having the conpressor start at the same time. The lift is 23amps and the compressor is 17.5amps. And then whatever the lights are. This would be unlikely but the most possible I would think.

Stop raising the lift if the comp starts, don't start the lift if its running. I really doubt it would trip anyway.
 