Goodman GSXC no contactor?

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
Goodman GSXC (C stands for UC Controller or Comfortnet)

Decided to clean my coils and do a preemptive replacement of the capacitor and contactor. Best to do this early on a Saturday morning versus 10:30 at night while the wife is bitching at you.

Ordered the parts and removed the electrical cover. No contactor to be found. There is a relay on the control board but certainly does not look capable of controlling a 4 ton compressor.

Seems that the GSX model has the contactor but no control board. Looking for confirmation that the GSXC version does not have a contactor...
 
To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,014
Location
Peace Valley,mo
Uc control board takes the contactor. This unit is variable speed compressor and condenser fan motor. So the relay on the board doesn't take the lock rotor amps that a single speed compressor does. Mini split units have been doing this for years.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,097
Location
Rhode Island
I looked up the manual, the GSXC does not have a variable speed compressor, it's actually a 2-stage, single speed compressor. There is no inverter drive. Looking at the wiring diagram - that relay on the control board is taking the full brunt of running the compressor.
 
To avoid these ads, REGISTER NOW!
OP
G

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
that relay on the control board is taking the full brunt of running the compressor.


That's what I was afraid of. In my mind, that little relay is working hard for its money. Do you know if the reliability of this board/relay? Here in the deep south, thinking I should order a board to have on hand.
 