I have a goodman heat pump/ac unit that also has an emergency heat strip setup, that the fan is constantly running. I replaced the control board because I thought I saw some abnormal discoloration on it but even after the change it continues to constantly run the fan. What should I be looking at now.
 
To avoid these ads, REGISTER NOW!

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,172
Location
Arkansas
IF, you mean the condenser fan then I would guess probably a bad defrost board. You can force a defrost cycle and if the fan still runs then I would bet the board is bad.
If you mean the indoor blower then I would first check for 24v on the green t-stat wire. Thermostat could have a hung up relay. If not then possibly a sequencer is hung.
 
To avoid these ads, REGISTER NOW!

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,172
Location
Arkansas
Yes, sequencer or relay or blower delay board. Whichever type setup you have there is a contact burnt and holding it on/made switch.
 

rstiner

New member
Joined
Aug 17, 2020
Messages
1
Location
PA
I know this is an old thread but did you fix this I have the exact same problem. My evap fan keeps running. Same as before I replaced the Comp relay. The 24 volt coil shorted I replaced that. I can remove the therm and it keep running. Please let us know if you fixed it?
Goodman heat pump 2 ton gsx1433 Blower ARUF1824
 

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,172
Location
Arkansas
If the evap fan continues to run with tstat unhooked then the relay or switch is hung closed. Might be a small control board with a relay on it.
 