Goodman Heatpump condenser fail question

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
6,065
Location
Snow Hill NC
18 years old 3 ton single stage unit, a/c was running and all of a sudden I’m outside and all I hear is a whining noise fan isn’t running but smells bad like something is overheating or burning turned it off for about 20 minutes at the panel...turn back on same thing , cooling fan turns freely, capacitor looks ok not swollen...
Any idea where to look? Don’t want to call and pay emergency call, I have PTAC in the sunroom fan blowing cool air in the house, gonna get a small window unit for the master which I’ve been wanting for hurricane season anyway...
 
To avoid these ads, REGISTER NOW!

Dave Carney

Well-known member
Joined
Feb 18, 2005
Messages
318
Location
Derby, KS
If you've never had the fan motor replaced, that could be it, 18 years is a long time. I had one burn up like that on a Goodman heat pump about 15 years ago. Need to replace the capacitor if you change the fan motor...but, really you need a tech, unless you are like me with a new fan motor, capacitor, and contactor waiting for the day that they are needed.
 
OP
N

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
6,065
Location
Snow Hill NC
I will call a tech first thing Monday...like I said I have a PTAC and blowing air in the house, closed all the blinds and spare room doors..etc...98 with humidity factor tomorrow so want to keep that cool as much in as I can
 
To avoid these ads, REGISTER NOW!
OP
N

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
6,065
Location
Snow Hill NC
All the connections on the condenser look ok, just the smell of burnt something coming from the condenser....were cool inside for now. 1st world problems right?
 
OP
N

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
6,065
Location
Snow Hill NC
Everything is running good after 3 days, put the window unit back in the box for another day..$5000 for a Trane single stage 15 Seer unit... were gonna use this old girl until she can’t pump no more...
Still gonna get it serviced this summer, get the coils cleaned good and checked out.
 

99LeCouch

Well-known member
Joined
Apr 18, 2011
Messages
1,053
Location
Rochester, NY
Fan motor get overheated?

The fan motor in our central A/C went out after 15-16 years. $300 and an afternoon adapting a universal fan motor got us cool again.

Coil cleaning is fairly easy. Couple cans of cleaner, a hose, and 30 minutes. Now if the coils are packed with grass or other plant detritus, taking the case off is a bit more involved.
 
OP
N

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
6,065
Location
Snow Hill NC
By the time I buy the coil cleaner and meds to get of the pain in the *** of doing it, I would rather pay $150 to let somebody do it the right way...lol, I’ll have a glass of whiskey.
 