I have a Grandaire heat pump it is a model WJA4
The blower will not shut off unless I trip the breaker.The thermostat is set to auto and the blower runs continuously doesn't matter if it's set heat of cool. I would appreciate all help and troubling shooting tips
Thanks
 
To avoid these ads, REGISTER NOW!

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,451
Location
Beautiful Southern Maryland
Could be the thermostat. If you turn the thermostat to "off" will the blower stop ? Or disconnect it completely ? Otherwise you will need the manual and a wiring diagram to further troubleshoot.
 

Done That

Well-known member
Joined
Aug 18, 2017
Messages
601
Location
MO
As Bill said, disconnect the Tstat completly and then restore power to the unit. If the blower is still on you probably have a welded relay in the package unit. Otherwise a welded relay in the thermostat can be the culprit. You need to determine which end of the system is causing the issue by process of elimination.
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,555
Location
Eastern North Carolina
I had one do that this weekend. It was a sequencer in the heat strip area that had come apart, turning from normally open connection to normally closed when it broke. $10 fixed it. Look at some videos on YouTube for how they work.
 
Last edited:
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
I unhooked the thermostat and it keeps running so I assume I need to pull the outside panel off and start checking there
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,555
Location
Eastern North Carolina
As someone else said, it may very well be the fan relay acting up. I pointed out the sequencer issue I ran into because it was a weird event. You could try tapping on the surface next to the fan relay with an object to see if the vibration causes the relay to release and shut the fan off. If it does, replace the relay. Past this, it likely is circuit tracing time unless you see a broken wire or wire terminal. If there is a diagram in the unit, I usually take a picture of it then expand it out on my IPad so The wiring is easier to trace for my old eyes.
 

acmikee

Well-known member
Joined
Feb 2, 2005
Messages
301
Location
olympia, wa
disconnect your "R" wire that will eliminate the tsat and the wire. if its still on then the control board probably need to be replaced..
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Do you have the switch turned to on instead of auto on the thermostat?
Maybe try pulling green wire off of stat.
Is there a high limit switch someplace that could be stuck?
 
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
I unhooked the green wire a couple days ago at the thermostat and blower kept running will try the red wire tonight and see if that works
 

Done That

Well-known member
Joined
Aug 18, 2017
Messages
601
Location
MO
Document I see on the web says a WJA4 is a packaged AC unit, with option to add electric heat....that's not a heat pump. It's a Carrier/ICP unit, private branded for Baker Distributing I beleive.

I don't see any control board in it, just some heater relay(s) depending on how many kw of electric heat was field installed.

When the blower is stuck on is it putting out heat? or just blower air?
 
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
It's putting out just blower air now it will blow out hot or cold depending on what the thermostat is call for
 
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
So here is a pic of what is in the unit the relay at the top right corner is for the a.c. Compressor not sure which one is for the blower
 

Attachments

  • P_20181208_095241_LL.jpg
    P_20181208_095241_LL.jpg
    85.3 KB · Views: 22

Done That

Well-known member
Joined
Aug 18, 2017
Messages
601
Location
MO
The ones in the left are the heat relays, plus the little tan board is a rectifier pcb I believe.

I'm thinking a heater limit or relay is stuck and keeping the blower on as a safety so it doesn't overtemp.

I'm not up to speed enough in those to offer much help. Going to need a meter and wiring diagram to sort it. Follow the wires back from the blower and start there.
 
To avoid these ads, REGISTER NOW!
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
The thermostat wires all have 28 volts outside at the unit depending on what I have the thermostat set at heat or air except the brown wires they never have any voltage and whenI I had the heat set at the thermostat each of these had 110 volts
 

Attachments

  • 1544287272316986670593.jpg
    1544287272316986670593.jpg
    96 KB · Views: 11
  • P_20181208_113749_LL.jpg
    P_20181208_113749_LL.jpg
    67.2 KB · Views: 15
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
So is this relay here maybe bad one of the brown wires go to the relay the other to the blower
 

Attachments

  • P_20181208_114548_LL.jpg
    P_20181208_114548_LL.jpg
    67.1 KB · Views: 15

Done That

Well-known member
Joined
Aug 18, 2017
Messages
601
Location
MO
That tan little board snaps onto the relay below it.

If you remove the thermostat and ensure no inputs coming from that wiring then you should be able to verify the relay is stuck if the blower remains on. Might be able to swap those two relays as a simple test, doubt both are bad at the same time.
 

Done That

Well-known member
Joined
Aug 18, 2017
Messages
601
Location
MO
Second picture in your first post above looks to be a sequencer (two yellow wires) simple metallic timer/switch. This is the item an earlier poster said caused same issue in his unit.
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,555
Location
Eastern North Carolina
http://www.grandaireac.com/wp-content/uploads/2018/04/WJA4-42655170800.pdf

Looking at the diagram in this link, why does the indoor fan motor show low voltage wiring going directly to the motor? Is there a fan relay attached directly to the motor? Or is there a relay inside the motor itself? I have not run into this on an HVAC diagram before. New to me. Is there something I am not seeing? The legend does not call out a fan relay either. The heat relays do not show a fan relay as part of them either. Normally when heat strips are activated, the first sequencer in line normally turns the fan on.
 
Last edited:

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,555
Location
Eastern North Carolina
Not sure who the question is directed to, but if me, I got my sequencer at a local HVAC supply that has no issue selling to the homeowner or handyman. Mine was a double stack unit where the first stage turned the fan on first, then the heat strip. When the control voltage to it ceases, it turns off the heat strip first, then the fan, to allow some cool down of the air stream. I don’t remember the number of mine right off. They are available in a selection of functions and timings. The M numbers on the sequencer determine when each stage of the sequencer does it’s thing. Timings are marked on the units.
 
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
Thank You RJ I'll have to see if I can get it online been to some of the HVAC supply stores here and they only sell to HVAC companies
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,555
Location
Eastern North Carolina
Troy, in the picture below, the small green wire should be what turns the fan on from the thermostat. Shut the unit down by shutting off power to it, and then disconnect this small green 24 volt wire connection. Keep ends from touching anything else. Turn unit back on and see if fan then runs. Give it at least 6 timed minutes before doing anything else. Let us know what it does. You could possibly have a shorted control cable wiring connection keeping the fan on.

Also examine the control wiring coming to the unit from the house. Weed trimmers are control wiring killers.
 
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
Does anyone know who the manufacture. Of this is
 

Attachments

  • IMG_20181224_092116.jpg
    IMG_20181224_092116.jpg
    25.2 KB · Views: 3
  • IMG_20181223_132915.jpg
    IMG_20181223_132915.jpg
    125.9 KB · Views: 3
OP
T

TroyL

Member
Joined
Dec 4, 2018
Messages
13
Location
Daytona Beach
I have put in the numbers in search and nothing comes back that's close what web sites have you all used I've tried Google Amazon ebay and have not found the right one
 