PoorOwner
CA
found a roll of grey THHN 12 stranded for clearance price..
can I use it for neutral wire? It's a light gray, I thought it was white at first.
I did a quick search it seems grey is legit for neutral.
mm08822
For your purposes at a single family home grey is ok to mix with white neutrals.
PhysicsDude
Dallas, TX
Gray wire is typically used for "high voltage" (277v/480v) neutral wiring, to differentiate it from 120v/240v/208v neutral wiring.
Should be fine to use as a neutral in a house. Even in commercial buildings, the white/gray convention isn't kept very strictly, especially when most 277v lighting is wired with black/white/green MC cable..
Norcal
Legally anything 600 volts and under is considered low voltage.
The use of gray for a neutral is fine.
Jim greengo
Behind my house
:beer::beer::beer::beer:
teamextreme
Lakewood, CO
By code, neutrals can be identified by white or gray marking, which means adding white tape to a gray wire is redundant and unnecessary EDIT: and per mm's comment in post 10, which corrects me, it actually is not legal, so you shouldn't tape them. Thank you for reminding me of that.
mm08822
The same re-identification restriction that applies to grounding conductors applies to grounded conductors. Op's conductor size is #12. Re-identification at time of install only permitted with #4 or larger conductors. Cables and cords excluded from restriction.
No tape.
Ji m
The Northeast
Grey is perfectly fine for Neutrals,
the code says use White or Natural Grey for Neutrals,
the industry decided to make 120/208 White w/Black Red & Blue phases
and 277/480 Grey w/Brown Orange Yellow phases,
but that specific color code is not a part of the NEC's code requirements.
alfredeneuman
Fullerton, CA
277 sure feels like high voltage when it grabs a hold of you :shocking: :thumbup:
The voltage definitions have recently changed.
Instead of 600V, now any voltage under 1000 is considered to be low voltage.
Between 1000 and 35000 are medium voltage.
Anything over 35000 is considered to be high voltage.
The average voltage of the electric chair is only 2000V.