To avoid these ads, REGISTER NOW!

grey wire for neutral

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
found a roll of grey THHN 12 stranded for clearance price..

can I use it for neutral wire? It's a light gray, I thought it was white at first.

I did a quick search it seems grey is legit for neutral.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
For your purposes at a single family home grey is ok to mix with white neutrals.
 

PhysicsDude

Well-known member
Joined
Jan 28, 2013
Messages
805
Location
Dallas, TX
Gray wire is typically used for "high voltage" (277v/480v) neutral wiring, to differentiate it from 120v/240v/208v neutral wiring.

Should be fine to use as a neutral in a house. Even in commercial buildings, the white/gray convention isn't kept very strictly, especially when most 277v lighting is wired with black/white/green MC cable..
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Gray wire is typically used for "high voltage" (277v/480v) neutral wiring, to differentiate it from 120v/240v/208v neutral wiring.

Should be fine to use as a neutral in a house. Even in commercial buildings, the white/gray convention isn't kept very strictly, especially when most 277v lighting is wired with black/white/green MC cable..

Legally anything 600 volts and under is considered low voltage.


The use of gray for a neutral is fine.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Gray wire is typically used for "high voltage" (277v/480v) neutral wiring, to differentiate it from 120v/240v/208v neutral wiring.

Should be fine to use as a neutral in a house. Even in commercial buildings, the white/gray convention isn't kept very strictly, especially when most 277v lighting is wired with black/white/green MC cable..
:beer::beer::beer::beer:
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
By code, neutrals can be identified by white or gray marking, which means adding white tape to a gray wire is redundant and unnecessary EDIT: and per mm's comment in post 10, which corrects me, it actually is not legal, so you shouldn't tape them. Thank you for reminding me of that.
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
The same re-identification restriction that applies to grounding conductors applies to grounded conductors. Op's conductor size is #12. Re-identification at time of install only permitted with #4 or larger conductors. Cables and cords excluded from restriction.

No tape.
 
To avoid these ads, REGISTER NOW!

Ji m

Well-known member
Joined
Nov 15, 2017
Messages
579
Location
The Northeast
Grey is perfectly fine for Neutrals,

the code says use White or Natural Grey for Neutrals,

the industry decided to make 120/208 White w/Black Red & Blue phases
and 277/480 Grey w/Brown Orange Yellow phases,

but that specific color code is not a part of the NEC's code requirements.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
277 sure feels like high voltage when it grabs a hold of you :shocking: :thumbup:

The voltage definitions have recently changed.
Instead of 600V, now any voltage under 1000 is considered to be low voltage.
Between 1000 and 35000 are medium voltage.
Anything over 35000 is considered to be high voltage.
The average voltage of the electric chair is only 2000V.
 
To avoid these ads, REGISTER NOW!