Any problems having 2 ground bars (one on each side of the box). I would like to run the wires as neatly as possible. If its ok, should I run a copper bridge wire to connect the 2 or is the box a good enough conductor (they would both be screwed right to the box). I can't seem to find any examples so I wanted to make sure I wasn't overlooking a problem.
 
To avoid these ads, REGISTER NOW!

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
Just screw them down on both sides of the box. No jumper needed. I most always use 2 when converting a main panel to a sub panel, as the original grounds usually won't all reach one bar. No connection to the neutral in a sub panel (don't forget). ;)
 

PRH44

Well-known member
Joined
Dec 25, 2009
Messages
563
Location
Indiana
Be sure to remove the paint underneath the bar. Drill and tap the connection or through bolt. Sheet metal screws are prohibited.
 
To avoid these ads, REGISTER NOW!
OP
N

n2ocamaro

Well-known member
Joined
Aug 3, 2011
Messages
183
Location
Clarksville, IN
Be sure to remove the paint underneath the bar. Drill and tap the connection or through bolt. Sheet metal screws are prohibited.
Thanks for the reminder on the paint. I am going to use the screws that came with the bars and drill/tap.
 