Ground/Hot Reversed

Coach James

Well-known member
Joined
Jun 24, 2005
Messages
8,934
Location
Sandhills of North Carolina
Hey guys,

Last week I had an outlet start malfunctioning. My circuit tester says ground and hot reversed. Outlet worked fine for years and is wired correctly.

Any ideas what could be the culprit? Loose wire somewhere else in the circuit?

Thanks
Coach
 
To avoid these ads, REGISTER NOW!

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,321
Location
Coastal NJ
Hey guys,

Last week I had an outlet start malfunctioning. My circuit tester says ground and hot reversed. Outlet worked fine for years and is wired correctly.

Any ideas what could be the culprit? Loose wire somewhere else in the circuit?

Thanks
Coach
It is backstabbed?
Check connections at this outlet and the one upstream that feeds it.
What type of malfunctioning?
Take voltage measurements from hot to neutral, hot to ground, neutral to ground, etc.
 
OP
C

Coach James

Well-known member
Joined
Jun 24, 2005
Messages
8,934
Location
Sandhills of North Carolina
Thanks for the responses, guys. I got it squared away. Just for kicks, I hooked the new outlet up the same as the old outlet and got the same problem. I started checking voltages across the new outlet's hot, neutral and ground and got it working correctly. All other outlets on the circuit were good, just this one started acting up after 20+ years of working fine.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Thanks for the responses, guys. I got it squared away. Just for kicks, I hooked the new outlet up the same as the old outlet and got the same problem. I started checking voltages across the new outlet's hot, neutral and ground and got it working correctly. All other outlets on the circuit were good, just this one started acting up after 20+ years of working fine.
So what was the issue?
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,802
Location
doo dah, kansas, usa
Thanks for the responses, guys. I got it squared away. Just for kicks, I hooked the new outlet up the same as the old outlet and got the same problem. I started checking voltages across the new outlet's hot, neutral and ground and got it working correctly. All other outlets on the circuit were good, just this one started acting up after 20+ years of working fine.
Checking voltages doesn't usually fix stuff. What did you alter to fix it?
 
OP
C

Coach James

Well-known member
Joined
Jun 24, 2005
Messages
8,934
Location
Sandhills of North Carolina
On the old outlet that started not working, the hot and neutral were connected to the correct respective sides of the outlet. Both wires were attached to the hot and neutral terminals closest to the same outlet. If I remember correctly, voltage across hot and neutral was 0, across neutral and ground was 120, hot and ground was 120. Outlet would not power anything, despite having done so for years.

When I put in a new outlet, I left the hot closest to one outlet and moved the neutral closest to the other outlet. After doing so hot/neutral read 120, hot/ground was 120 and neutral/ground was 0. Circuit tester read "Correct".

The old outlet was back stabbed. The new one, I connected to the screw terminals.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
On the old outlet that started not working, the hot and neutral were connected to the correct respective sides of the outlet. Both wires were attached to the hot and neutral terminals closest to the same outlet. If I remember correctly, voltage across hot and neutral was 0, across neutral and ground was 120, hot and ground was 120. Outlet would not power anything, despite having done so for years.

When I put in a new outlet, I left the hot closest to one outlet and moved the neutral closest to the other outlet. After doing so hot/neutral read 120, hot/ground was 120 and neutral/ground was 0. Circuit tester read "Correct".

The old outlet was back stabbed. The new one, I connected to the screw terminals.


No clue what any of this means.
 
To avoid these ads, REGISTER NOW!
OP
C

Coach James

Well-known member
Joined
Jun 24, 2005
Messages
8,934
Location
Sandhills of North Carolina
No clue what any of this means.
It is a duplex outlet with a ground, 2 hot terminal screws and 2 neutral terminal screws. One hot and neutral is closer to one outlet and the other hot and neutral are closer to the other outlet. The original outlet had the hot and neutral connected to the terminals closest to the same outlet. Outlet worked for years then stopped. When I replaced the outlet, I connected the hot closest to one outlet and the neutral closest to the other outlet. Outlet now works.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
It is a duplex outlet with a ground, 2 hot terminal screws and 2 neutral terminal screws. One hot and neutral is closer to one outlet and the other hot and neutral are closer to the other outlet. The original outlet had the hot and neutral connected to the terminals closest to the same outlet. Outlet worked for years then stopped. When I replaced the outlet, I connected the hot closest to one outlet and the neutral closest to the other outlet. Outlet now works.
What you described should have no bearing on functionality.

Makes me worried you wired it totally wrong.
 
OP
C

Coach James

Well-known member
Joined
Jun 24, 2005
Messages
8,934
Location
Sandhills of North Carolina
What you described should have no bearing on functionality.

Makes me worried you wired it totally wrong.
It's hooked up green to ground, black to hot terminal and white to neutral. Circuit tester says it's correct. DMM reads 120 in both outlets.

I've replaced scores of outlets and it never mattered which hot or neutral I used. I don't know why this one seemed to be different.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
It's hooked up green to ground, black to hot terminal and white to neutral. Circuit tester says it's correct. DMM reads 120 in both outlets.

I've replaced scores of outlets and it never mattered which hot or neutral I used. I don't know why this one seemed to be different.
Did you check both halves of the duplex with the tester?.

Almost sounds like you were testing one side and the tab connecting the two was broken.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,160
Location
Modesto, CA
Did you check both halves of the duplex with the tester?.

Almost sounds like you were testing one side and the tab connecting the two was broken.
yeah the only way he could have this issue was the tab on the side was broken off.... impossible for that to happen unless someone messed with the receptacle
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
yeah the only way he could have this issue was the tab on the side was broken off.... impossible for that to happen unless someone messed with the receptacle
Or by chance when he first connected it there want proper contact, then by moving wires and connected correctly.
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,802
Location
doo dah, kansas, usa
What you described should have no bearing on functionality.

Makes me worried you wired it totally wrong.
If there was something else plugged in like a lamp somewhere on the branch, it could provide continuity so the would appear to be 120 on neutral. The placement of the wires "closer to one outlet or the other" has no bearing on it except that on the original outlet, the backstabbed wires probably developed a bad connection which is why stuff stopped working.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,321
Location
Coastal NJ
New theory:

Since the house has backstabbed outlets, perhaps the outlet upstream of the one you replaced has an issue. And it was just coincidence that it started working again during your repair efforts.
 

Meursault74

Well-known member
Joined
Apr 1, 2019
Messages
22,274
Location
Southern California
Is it a GFCI?
My brother had GFCI outlet that stopped working in his kitchen. I found the hot and ground "reversed reading" when I used a plug tester.. DMM gave the same results at the plugs. The wires were not reversed. The bare wires not connected to the outlet gave the correct readings. I had a spare normal outlet and put it in and it was fine. When he bought a new GFCI I swapped it out and it that one was fine. Something wrong with the internals of the original GFCI, but I didn't open it up to look. I don't believe there was current through the ground, as someone would have likely been shocked as there was a grounded toaster oven plugged in. Curious as to why the readings.
 