I just bought this house I'm in now.It was built in the 60's.All the plugs only have the old style 2 prong outlets(no 3rd for ground).How do I need to go about changing these out so I have proper grounding?
 
To avoid these ads, REGISTER NOW!

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,589
Location
oklahoma
No need to change wiring to get shock protection. Just install a GFCI on each circuit so that all downstream recepts are protected or install GFCI breakers. Change all recepts to 3 prong and be sure in install the mandated stickers indicating the lack of true ground.
 

matt151617

Well-known member
Joined
Dec 17, 2011
Messages
488
Location
New Jersey
Many times the box itself is grounded. Carefully touch the red probe of a multimeter to the hot (black wire) side of the outlet, and the black probe to the metal box. If it shows 120v, you can swap in a new 3 prong outlet. Just make sure to add a seperate ground wire... they sell pigtails with the screw already attached for this purpose.
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Many times the box itself is grounded. Carefully touch the red probe of a multimeter to the hot (black wire) side of the outlet, and the black probe to the metal box. If it shows 120v, you can swap in a new 3 prong outlet. Just make sure to add a seperate ground wire... they sell pigtails with the screw already attached for this purpose.
Not true in all cases. This can be very unsafe.
If there is older metallic cable without the bond strip he will get a ground reading, but NO proper grounding means exists.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The condition of the wire may be a factor, not every device needs a grounded circuit. Sometimes its about as easy to run a new wire for one to the point its needed in remodel. My Dads house, early 60's, just before 3 wire, any additions we run a new wire or modify a couple crucial circuits, laundry, bath, counter tops, lights, switch loops we leave alone as well as many unused 2 wire recepts. Got a lamp in it they never turn on.

As for major appliances I recall they had a combined circuit for range oven, as I recall disconnected it, fed it with the old dryer circuit, it was 240, ran a new 4 wire to the oven and replaced the 3 for a 4 on the dryer. Cost 2 breaker spaces and one cable.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Many times the box itself is grounded. Carefully touch the red probe of a multimeter to the hot (black wire) side of the outlet, and the black probe to the metal box. If it shows 120v, you can swap in a new 3 prong outlet. Just make sure to add a seperate ground wire... they sell pigtails with the screw already attached for this purpose.

In a wood framed house, steel boxes nailed to the studs, and old two wire wo/grd Romex supplying it, you don't have a ground, no matter what your meter might show.

Charles
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
Depending on when in the sixties the house was built, there may be a grounding conductor but if there is one, it will be 16 AWG if NM cable.
 