I plan on putting a 60 amp breaker in the box in the house and run 2-2-2-4 AL URD underground in conduit to my detached garage.
URD is not permitted inside a structure.
Are you transitioning to another cable type on each end?
MHF would be easier as its permitted inside...
I had to upsize the wire size because it is an 85 ft run to the panel in the garage.
85' is not that long of a run.
you could put #2 al on a 90a breaker and not have issues with voltage drop.
I'm going to have my ground attached to the ground in the house and the ground in the garage panel. My question is do I need to add a ground rod at the garage? I've been reading varied opinions.
Thanks
You are confusing 2 different things. An EGC aka ground wire, that goes between the panels, is NOT the same thing nor has the same function as a grounding electrode. DO NOT confuse the 2.
The EGC between panels is to provide a low impedance fault current pathway.
Grounding electrodes do not and cannot do this. They are for grounding lightening, limiting voltage to earth, and shunting higher voltage primary lines when they contact secondary lines.
YES! you definitely need grounding electrodes. code requires 2 unless you can prove 25ohms or less resistance to earth with one.
Also, not sure why or where you're getting varied "opinions" on this as this is a VERY clear topic. I'm thinking you're getting info from people who don't understand basic concepts and differences between
Equipment
Grounding
Cconductors & grounding electrodes.
NO! The reason there are 4 conductors is one of them is for ground.
Also, you don't want URD, you want MHF ! It is also cheaper.
Completely WRONG. Come'on. youve been here long enough to know this.
The EGC between panels is not for shunting lightening.
you are confusing 2 different things.