Ground Rod for All Sub Panels?

BentBierz

Well-known member
Joined
Dec 3, 2014
Messages
188
Location
Alvin, TX (Houston Metro Area)
Hello,

I am getting new metered power run to a detached building and will have several sub panels inside the building coming off of the main panel. One panel is for general lighting, outlets, bench top equipment, etc. I will also have a panel coming off of a Phase Perfect digital phase converter to supply 3 phase power for up to 5 pieces of equipment.

Question: Regardless of use, is it required to have each sub panel in a building attached to a grounding rod or is the requirement only for the main panel? Thanks.
 
To avoid these ads, REGISTER NOW!

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
Ground electrode is needed only at first main disconnect at each structure.

Then each subsequent panel would have a ground wire running from the ground terminal block of the main panel to the ground terminal block of the sub panel, right?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
Ground rods aren't required for each panel. Ground rods are required for each building.
 
Last edited:
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
Then each subsequent panel would have a ground wire running from the ground terminal block of the main panel to the ground terminal block of the sub panel, right?

Not necessarily a wire
Running EMT, Rigid Metal, or Intermediate Metal Conduit between them would bond them.

(Bert, he's speaking of panels within the same building :))
 
OP
B

BentBierz

Well-known member
Joined
Dec 3, 2014
Messages
188
Location
Alvin, TX (Houston Metro Area)
(Bert, he's speaking of panels within the same building :))

Yes, new service from the pole to a steel building. I know that there needs to be a ground rod (or two) at the main panel but was curious if you had multiple subpanels off of this main panel, do they ALL need ground rods? I have searched on several electrical forums and so far have seen several people that said you DIDN'T need a rod at every subpanel. Unfortunately, they made definitive statements but did not provide a code cite.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,010
Location
NJ
Yes, new service from the pole to a steel building. I know that there needs to be a ground rod (or two) at the main panel but was curious if you had multiple subpanels off of this main panel, do they ALL need ground rods? I have searched on several electrical forums and so far have seen several people that said you DIDN'T need a rod at every subpanel. Unfortunately, they made definitive statements but did not provide a code cite.

You won't find a code requirement stating where not needed, but you will find where needed.

Needed at the point of service disconnect from utility and each separate structure fed with a sub-panel thereafter.
 
OP
B

BentBierz

Well-known member
Joined
Dec 3, 2014
Messages
188
Location
Alvin, TX (Houston Metro Area)
You won't find a code requirement stating where not needed, but you will find where needed.

Needed at the point of service disconnect from utility and each separate structure fed with a sub-panel thereafter.

Makes sense! I have been a Coast Guard vessel inspector and inspections branch chief for many years. We teach all new inspectors that if you "can't cite it, don't write it!"
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,049
Location
Modesto, CA
Yes, new service from the pole to a steel building. I know that there needs to be a ground rod (or two) at the main panel but was curious if you had multiple subpanels off of this main panel, do they ALL need ground rods? I have searched on several electrical forums and so far have seen several people that said you DIDN'T need a rod at every subpanel. Unfortunately, they made definitive statements but did not provide a code cite.

thats not how the code works. If it doesnt say something is required then its not required. The code will not say when something ISNT required.
 
OP
B

BentBierz

Well-known member
Joined
Dec 3, 2014
Messages
188
Location
Alvin, TX (Houston Metro Area)
thats not how the code works. If it doesnt say something is required then its not required. The code will not say when something ISNT required.

Makes sense! I have been a Coast Guard vessel inspector and inspections branch chief for many years. We teach all new inspectors that if you "can't cite it, don't write it!"

Believe I stated as much above!
 