ground rod hit rock need advise

To avoid these ads, REGISTER NOW!

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Let's say you try a few locations and all are hitting bedrock. The next thing to do is use a ground plate or plane. That will be a large piece of metal that is buried as deep as you can get it. Some are made of soldered/welded bar, some are plates with holes punched in them.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
If you have rebar in your slab, you can find a spot to punch in and tie on to the rebar for a UFER ground. It's rough but doable.
 

chickenhauler

Well-known member
Joined
May 31, 2011
Messages
473
Location
Pennsylvania
All I have is rock around my shop. Had I known ahead of time that I could have put the rods in my footer, I would have. I ended up laying mine in little trenches then covering them up. Who knows how much "grounding" a rod is going to do in a pile of sandstone, but the inspector was happy with it.
 

The_Tango

Active member
Joined
Dec 12, 2010
Messages
41
Location
Knoxville, TN
Drive it in at an angle, say 30 degrees off vertical - Sometime that will allow it to veer off if it contacts something
 

ert01

Well-known member
Joined
Jun 26, 2011
Messages
151
Like mentioned, try again at an angle or just bury a ground plate instead of a rod. Doesn't need to be nearly as deep. Check your laws though as I'm sure ours are different up here in Canada.

What are you using to install the rod? A big hammer drill and a cup attachment or the clamp on attachment is preferable and you'd be surprised at what you could put a rod through with one of those.

Also for anyone else, if the ground is frozen try "lubricating" the rod with some antifreeze. They drive like butter then.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
go to a equipment rental place,rent an electric jackhanner.they have a socket that will go over the rod.done it many times.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,921
Location
oregon
If you have rebar in your slab, you can find a spot to punch in and tie on to the rebar for a UFER ground. It's rough but doable.

When I built the ufer had to be inspected and tagged before pouring the concrete so check with the inspector. That said, where are you in the building process? You have the option of a ufer ground, laying the ground rod in a trench, and as others have said a ground plate. I would suggest talking with the building inspector and ask what to do as I'm sure that others in the area have had to deal with the same issue.

lg
no neat sig line
 

rwreuter

Well-known member
Joined
Feb 21, 2011
Messages
243
Location
Mulvane, Kansas
the building inspector isn't the person that has to buy off on it...it is the electrical inspector.

in accordance with the NEC you can drive the ground(S) (2) up to a 45 degree angle (6' apart)

the pros (larger contractors) have Hilte's that drive the rods down into the ground. first we try to drive them in vertical and if that doesn't work then up to 45 degrees. that usually works. you can rent these from rent-a centers or Lowes or Home Depot.

word of caution..if you use a Hilte, put the DB (direct burial) clamp on first...the Hilte will mushroom the ground rod and you won't be able to get the clamp on.

concerning that plate, i have never seen one installed (of course that is not to say that it isn't done. when i built my house i drove 2 ground rods and used a ufer ground also.
 
OP
M

mebedave

Well-known member
Joined
Jan 17, 2010
Messages
260
Location
Atlantic county area, New Jersey USA
To late for ufer ground, slab is in already. although my jib crane could be used as a ufer ground i guess. The footing for the jib sets on the rock layer which I drilled and drove lots of rebar into the rock and the anchor bolts for the jib are welded to the rebar. Only problem here is the jib would be about 20' from the panel. would that work?? I can try to drive at a 45 degree, but I know for a fact the rod will hit rock at about 2 foot will that be deep enough if i can get the rod driven at a 45. Question if you have a ground rod or two why and what is a ufer (i know its rebar from your footing but why)
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
>To late for ufer ground, slab is in already.
Just for fun - In the large city close to here, the inspectors will MAKE you jackhammer into the slab if there is no rebar sticking out for a UFER. There is no "too late for that". In fact, that city requires TWO methods, one of which must be a UFER.

UFER is a grounding system discovered around WWII. Concrete is conductive, so your slab and rebar sitting on the ground is one big fat ground connection. I used 20' of #4 copper in the slab.
 
Last edited:

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
it always irks me that inspectors are constantly missing the fact that ufer ground is not optional. If you have a footer with rebar in it, you HAVE to bond the rebar...(on new construction, and inspector has to sign off on it before the pour
 
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
it always irks me that inspectors are constantly missing the fact that ufer ground is not optional. If you have a footer with rebar in it, you HAVE to bond the rebar...(on new construction, and inspector has to sign off on it before the pour

Hmmm - comments because that seems to not be the way 2011 reads. See #3, what I based my one electrode on (#3, sub 2):

"
250.52 Grounding Electrode Types.
(A) Electrodes Permitted for Grounding.
(1) Underground Metal Water Pipe Electrode. Underground metal water pipe in direct contact with the earth for 10 ft or more can serve as a grounding electrode.
(2) Metal Frame Electrode. The metal frame of a building/structure can serve as a grounding electrode when it meets at least one of the following conditions:
(1) At least one structural metal member is in direct contact with the earth for 10 ft or more, with or without concrete encasement.
(2) The bolts securing the structural steel column are connected to a concrete encased electrode [250.52(A)(3)] by welding, exothermic welding, steel tie wires, or other approved means.
(3) Concrete-Encased Electrode. At least 20 ft of either (1) or (2):
(1) One or more of bare, zinc-galvanized, or otherwise electrically conductive steel reinforcing bars of not less than ½ in. diameter, mechanically connected together by steel tie wires, welding, or other effective means, to create a 20 ft or greater length.
(2) Bare copper conductor not smaller than 4 AWG.
The reinforcing bars or bare copper conductor must be encased by at least 2 in. of concrete located horizontally near the bottom of a concrete footing or vertically within a concrete foundation that’s in direct contact with the earth.
If multiple concrete-encased electrodes are present at a building/structure, only one is required to serve as a grounding electrode"
Note: Concrete containing insulation, vapor barriers, films or similar items separating it from the earth isn’t considered to be in “direct contact” with the earth.


Remainder for the OP's problem:
(4) Ground Ring Electrode. A ground ring consisting of at least 20 ft of bare copper conductor not smaller than 2 AWG buried in the earth encircling a building/structure can serve as a grounding electrode.
(5) Ground Rod and Pipe Electrode. Ground rod electrodes must not be less than 8 ft in length in contact with the earth [250.53(G)].
(b) Rod-type electrodes must have a diameter of at least 5⁄8 in., unless listed.
(6) Listed Electrode. Other listed grounding electrodes.
(7) Ground Plate Electrode. A bare or conductively coated iron or steel plate with not less than ¼ in. of thickness, or a solid uncoated copper metal plate not less than 0.06 in. of thickness, with an exposed surface area of not less than 2 sq ft.
(8) Metal Underground Systems Electrode. Metal underground piping systems, underground tanks, and underground metal well casings can serve as a grounding electrode.
 
Last edited:

rwreuter

Well-known member
Joined
Feb 21, 2011
Messages
243
Location
Mulvane, Kansas
(2) Metal Frame Electrode. The metal frame of a building/structure can serve as a grounding electrode when it meets at least one of the following conditions:

notice the conditions that need to be met to be forced to use a ufer....metal frame building.
 

rwreuter

Well-known member
Joined
Feb 21, 2011
Messages
243
Location
Mulvane, Kansas
see a ufer ground set up is supposed to be inspected BEFORE the concrete is poured to insure that a minium number of feet are tied together.

so if the inspector forces you to jack hammer and us a ufer ground he may be costing you a lot of money for no reason. the rebar may not be all be tied together PROPERLY.
 

rwreuter

Well-known member
Joined
Feb 21, 2011
Messages
243
Location
Mulvane, Kansas
To late for ufer ground, slab is in already. although my jib crane could be used as a ufer ground i guess. The footing for the jib sets on the rock layer which I drilled and drove lots of rebar into the rock and the anchor bolts for the jib are welded to the rebar. Only problem here is the jib would be about 20' from the panel. would that work?? I can try to drive at a 45 degree, but I know for a fact the rod will hit rock at about 2 foot will that be deep enough if i can get the rod driven at a 45. Question if you have a ground rod or two why and what is a ufer (i know its rebar from your footing but why)

distance is irrelavent....when you bond your water pipe and gas pipe i have often had to run clean across the house and into the under floor in order to get to within 10' of the entrance.

2' feet will not be deep enough....i guess you could dig a large ditch like someone else said and lay the rods out, as long as they are more than 6' feet apart i guess that would work. as a last resort, what i have done when i come to a serious problem area, i just call the inspector and explain the situation and let him make a recommendation. they usually are very helpful.

they will have an answer, because i can gurantee you that this isn't the only situation that has come up in your area.
 

rwreuter

Well-known member
Joined
Feb 21, 2011
Messages
243
Location
Mulvane, Kansas
not sure about that, just call the electrical inspector.....let him know what is going on....i didn't know it was a metal building...according the 2011 NEC you will have to have a ufer ground (that is of course if your AHJ has adopted the new code.

call him/her and let them know what the situation is....they will work with home owners much better than an electrical contractor.
 
OP
M

mebedave

Well-known member
Joined
Jan 17, 2010
Messages
260
Location
Atlantic county area, New Jersey USA
not sure about that, just call the electrical inspector.....let him know what is going on....i didn't know it was a metal building...according the 2011 NEC you will have to have a ufer ground (that is of course if your AHJ has adopted the new code.

call him/her and let them know what the situation is....they will work with home owners much better than an electrical contractor.

we do not have inspectors here (no Joke):beer:
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Seeing on it sounds like an inspector may be absent here run a number 4 to the footer steel of your crane, in all reality its probably as good as it gets. Well casing if I had it nearby or had steel water piping if possible.
 
Last edited:

planecrazy29

Well-known member
Joined
Oct 10, 2011
Messages
72
another note: should I some how ground my sheet metal on my pole building. If so how?

I believe you have to ground it. I'm not an electrician, but I work in an industry where we have had people get killed because metal buildings and/or siding was not grounded. If it's not grounded and it made hot somehow, you become the ground when you touch the metal. Even if it's not required, please ground it.
 
OP
M

mebedave

Well-known member
Joined
Jan 17, 2010
Messages
260
Location
Atlantic county area, New Jersey USA
I believe you have to ground it. I'm not an electrician, but I work in an industry where we have had people get killed because metal buildings and/or siding was not grounded. If it's not grounded and it made hot somehow, you become the ground when you touch the metal. Even if it's not required, please ground it.

thks planecrazy, Yes I need to find a why to ground the building.
 