Yes that's me. One electrician did the panel replacement and hooked up the 100 amp wires on both panels. Another electrician ( friend of family) helped me wire the shop. He said I needed the ground rod installed and hooked to the ground bar. Here is a zoomed in pic
Yeah that bar ties the left and right bars together.
That electrician didnt know what he was doing.
If he was old school, he wouldve omitted the green taped wire, and done it as a 3-wire panel, which wouldve been wrong but current as of 2005 code.
The way its done now sets up a potential for someone to get shocked.
So u need to:
Remove green bonding screw
buy ground bar kit that is listed for that panel(check panel label)
screw it into pre-punched holes in panel using included self taping screws
move green taped EGC and green ground wires over to new bar
pound 2 ground rods and run GEC from rods to new bar. U can use solid #6 for the GEC
AND tell that electrician he needs to get updated on current code
here is a diagram
This is the wire that was used.
I wasnt referring to the branch circuit wiring. I was referring to the main feeder wires- the ones with the neutral that has the yellow stripe.
That is URD and is most likely not rated for indoor use.
And looks like u have 20 breakers. Did u use #14 on the 20a breakers? If so that is incorrect as well.