I will be running my electircal in EMC. One conduit will contain more than one circuit. Can the two circuits share a common ground wire or do I need to run a separate ground for each circuit????


Reb
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,680
Location
Maine
I will be running my electircal in EMC. One conduit will contain more than one circuit. Can the two circuits share a common ground wire or do I need to run a separate ground for each circuit????


Reb

They can share.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
As long as its sized for the largest circuit. Its one of the advantages of piped wiring. Some dont even need ground wire, the pipe may be sufficient.
 
To avoid these ads, REGISTER NOW!

ArthurPE

Banned
Joined
Jun 14, 2009
Messages
423
it's usually EMT electrical metallic tubing or IMC, intermediate metallic conduit
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
I think he is talking about the neutral wire.

A lot of guys confuse ground and neutral.
 