Grounding 2 gang Duplex

scout4bta

Well-known member
Joined
Nov 2, 2017
Messages
90
Location
Willcox Arizona
When tying the grounds in a 2 gang duplex do I need to tie the ground wires together and to the box or can I tie the gnd to each duplex as I've done. This is a detached steel workshop. I would think that the with all the 'steel' that that would be sufficient grounding.
The box is for led lighting on the ceiling.
 

Attachments

  • DSCN1457 copy.jpg
    DSCN1457 copy.jpg
    76 KB · Views: 209
Last edited:
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,583
Location
Fullerton, CA
All the grounding wires need to be attached to each other. (w/wirenuts or crimp connectors)
There is a 10-32 threaded hole in the back of the box, which is meant for a ground screw.
You've got to ground (bond) the box, and both of the receptacles as well
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
To add to this if the devices were screwed in to the box it may be done differently but with the detached cover it needs a wire to the box too.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,755
Location
NW Iowa
Removing a device should not interrupt the ground path. Plus your box needs a ground screw and jumper.

If those are self grounding receptacles then you could simply ground the metal box and forgo the wire to the receptacle.

For stuff like this I really like just using the pipe ground instead of running a wire. eliminates so much work and the pipe is a better conductor anyway.
 

ford33

Well-known member
Joined
Feb 26, 2011
Messages
2,118
Location
Chicago, IL. USA
With EMT used from the breaker box to the metal receptacle boxes why is it necessary to have a separate ground wire to the receptacles? This is assuming self grounding receptacles and well constructed EMT installation.
 
OP
S

scout4bta

Well-known member
Joined
Nov 2, 2017
Messages
90
Location
Willcox Arizona
Yes these are self grounding outlets. All wiring is in metallic conduit. So according to 'code' I can forgo the gnd wire to the outlets but tie the gnd wires together along with a gnd wire from the box?
 

ford33

Well-known member
Joined
Feb 26, 2011
Messages
2,118
Location
Chicago, IL. USA
i am not a licensed electrician but I am familiar with this installation. If metal conduit is used everywhere a separate ground wire is not necessary. I do not use a ground wire to the outlets. They are grounded when installed in the metal box.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Yes these are self grounding outlets. All wiring is in metallic conduit. So according to 'code' I can forgo the gnd wire to the outlets but tie the gnd wires together along with a gnd wire from the box?

No, you can eliminate the ground wires being pulled through the conduit. The conduit serves as the "ground wire". The receptacles still need to be grounded. Since you have self grounding outlets they would not need any ground wire IF you are using a mud-ring to install them. For a raised cover installation, which you are using, it will require ground jumpers from the receptacles to a ground screw mounted in the box.
 
OP
S

scout4bta

Well-known member
Joined
Nov 2, 2017
Messages
90
Location
Willcox Arizona
No, you can eliminate the ground wires being pulled through the conduit. The conduit serves as the "ground wire". The receptacles still need to be grounded. Since you have self grounding outlets they would not need any ground wire IF you are using a mud-ring to install them. For a raised cover installation, which you are using, it will require ground jumpers from the receptacles to a ground screw mounted in the box.
I did not mean to imply not pulling the ground wire through conduit, I definitely have the ground wire in conduit. I was talking about not connecting the gnd wires to the outlet because the outlets are self grounding, connecting the gnd wire to the box and also to the gnd wires.
 

rabidsquirrel

Well-known member
Joined
Jul 17, 2010
Messages
397
Location
SE Pennsylvania
No, you need a ground wire from the receptacles to the box. Once you pull that cover off the receptacles are no longer grounded if you rely on the self grounding feature.

Sent from my VS987 using Tapatalk
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,216
Location
SE MI
Removing a device should not interrupt the ground path. Plus your box needs a ground screw and jumper.

If those are self grounding receptacles then you could simply ground the metal box and forgo the wire to the receptacle.

Is this still legal ? Maybe I have been using too many plastic boxes !
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,583
Location
Fullerton, CA
To qualify for grounding (without the jumpers) both the box and the cover need to be listed for grounding path with each other.
Each listing costs about $20K and the listing is just for that particular box/cover combination.
That's why few (I know of none) are listed.
 
Last edited:

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I did not mean to imply not pulling the ground wire through conduit, I definitely have the ground wire in conduit. I was talking about not connecting the gnd wires to the outlet because the outlets are self grounding, connecting the gnd wire to the box and also to the gnd wires.

We know what you were implying. What teamextreme is trying to say is, you do not need to pull a ground wire through conduit. You could pull all of the ground wires out of your conduit right now, and you'd still be code-compliant. This is because the conduit itself can act as a ground conductor, as long as you have a continuous metallic path all the way back to the panel. If you do decide to remove the ground wires, all you would have to do is run a ground wire from the receptacle to the ground screw on the box.

Of course you can keep the ground wires in the conduit if you want. In that case, install a jumper to the screw on the box and jumpers to each receptacle and tie them all together.
 
To avoid these ads, REGISTER NOW!

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
To summarize:

1)Pull the green ground wires out and save them for a rainy day.

2) Buy green grounding screws and put them in the threaded hole in the box marked "GND" and run pigtails from the green grounding screws you have just installed on the boxes to the green screws on the outlets.

3) Make sure your conduit is grounded and connected properly to all boxes so that it acts as ground back to the source.
 
OP
S

scout4bta

Well-known member
Joined
Nov 2, 2017
Messages
90
Location
Willcox Arizona
Even bought the green ground screws.
Every thing is grounded.
Only have 5-6 more to go.
 

Attachments

  • DSCN1459.jpg
    DSCN1459.jpg
    116.7 KB · Views: 85

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,755
Location
NW Iowa
No, you can eliminate the ground wires being pulled through the conduit. The conduit serves as the "ground wire". The receptacles still need to be grounded. Since you have self grounding outlets they would not need any ground wire IF you are using a mud-ring to install them. For a raised cover installation, which you are using, it will require ground jumpers from the receptacles to a ground screw mounted in the box.

Since the raised cover he is using have the recessed corners you do not have to jumper the receptacle to the box. The recessed corners provide a solid connection compared to raised covers without.

There is reference to this in the NEC but I'd have to do some digging to find the section
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
No, you can eliminate the ground wires being pulled through the conduit. The conduit serves as the "ground wire". The receptacles still need to be grounded. Since you have self grounding outlets they would not need any ground wire IF you are using a mud-ring to install them. For a raised cover installation, which you are using, it will require ground jumpers from the receptacles to a ground screw mounted in the box.

:thumbup::thumbup:
 

egdede

ALLIANCE MEMBER
Joined
Dec 20, 2009
Messages
2,094
Bert, why do you say conduit is a better conductor than copper wire?
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
They tested this, some reason about fields and such stuff I don't know much about but it trips the breaker faster. Either is legal.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,904
Bert, why do you say conduit is a better conductor than copper wire?

Huge cross section gives it much lower impedance. The purpose of the safety ground is to flow enough current to trip the breaker in the event of the short, and do it fast. Metal conduit does that better than copper wire; even if a ground wire is present, the conduit will carry the majority of the fault current. Grounds are used by people who don't believe that, and for redundancy (if the conduit it broken, it won't clear a fault, and will shock you.) in industrial and outdoor applications.
 

egdede

ALLIANCE MEMBER
Joined
Dec 20, 2009
Messages
2,094
I'm surprised...In the future, I suspect I'll still pull a wire through existing conduit out of an abundance of caution.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Since the raised cover he is using have the recessed corners you do not have to jumper the receptacle to the box. The recessed corners provide a solid connection compared to raised covers without.

There is reference to this in the NEC but I'd have to do some digging to find the section

No, you still need to use a pigtail from each receptacle to the box, when using ANY raised covers. If the corner cover screws become loose, bonding is compromised. The NEC reference has to do with FLUSH (in-wall) mounted devices making solid contact with the metallic box. No ground wire is needed in that case.

Steve
JW
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,755
Location
NW Iowa
No, you still need to use a pigtail from each receptacle to the box, when using ANY raised covers. If the corner cover screws become loose, bonding is compromised. The NEC reference has to do with FLUSH (in-wall) mounted devices making solid contact with the metallic box. No ground wire is needed in that case.

Steve
JW

250.146(A) says you don't have to if the recepacle is attached to the cover with at least two screws and when the cover screws are located in a non raised portion.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
250.146(A) says you don't have to if the recepacle is attached to the cover with at least two screws and when the cover screws are located in a non raised portion.

No. The exception doesn't say "device attached with two screws", it says two PERMANENT fasteners, such as RIVITS, or a thread locking means.

I agree about the flattened corners of the cover, meeting the first half of the exception, but the second part talks about a LISTED box AND cover combination, providing satisfactory ground continuity.

Steve
JW
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,990
Location
NJ
no. The exception doesn't say "device attached with two screws", it says two permanent fasteners, such as rivits, or a thread locking means......continue reading the rest of the article.

i agree about the flattened corners of the cover, meeting the first half of the exception, but the second part talks about a listed box and cover combination, providing satisfactory ground continuity.

Steve
jw

250.146A.JPG

and the mfr's spec sheet.......no jumper required.

902C_Notes.JPG
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
250.146A.JPG

and the mfr's spec sheet.......no jumper required.

902C_Notes.JPG

You are 100% correct, IF you are using Raco ( or other approved ) covers.

Not all covers come with lock washers. Steel City RS-12's come with stamped steel nuts (no LW's )

I'll always put the jumper in, just so I'm covered

Steve