Grounding Cabinets and Tables

Cecell

Active member
Joined
Feb 17, 2024
Messages
26
Location
Missouri
In my new shop I need to ground my yellow fire cabinet and want to go ahead and ground my metal working surfaces while I'm at it since I do tinker with microcontrollers and such on occasion.

All receptacles use those blue plastic in-wall stud mounted boxes and are wired with Romex 12/2 w/ground and all metal objects make contact with concrete floors that are poured directly into dirt.

Now, question: Can I ground objects by connecting them to the ground wire that runs to a receptacle? The goal closest to my brain at the moment is mitigating static electricity. The GFCI of the receptacles powering tools would catch any device faults right?
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,299
Location
Coastal NJ
Be careful with grounding workbenches. An ESD workbench is designed to dissipate static. It has a high impedance grounding system as does the ESD wrist straps. This is not a low impedance ground as that can present an electrocution hazard.
Imagine one hand on a grounded work bench and the other touching something live inside an electronic device.

There are ESD mats you can place on a wood bench.

Read up on ESD as mentioned above.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,311
Location
Illinois near St. Louis, Missouri
Be careful with grounding workbenches. An ESD workbench is designed to dissipate static. It has a high impedance grounding system as does the ESD wrist straps. This is not a low impedance ground as that can present an electrocution hazard.
Imagine one hand on a grounded work bench and the other touching something live inside an electronic device.

There are ESD mats you can place on a wood bench.

Read up on ESD as mentioned above.
This. ^ Grounded metal benches are a shock hazard if working on live electrical things. Even with low voltage stuff I would want a high impedance ESD mat. That way if a conductor touches the surface it has much less chance of damage to the circuit. I think some rules for grounding flammable storage require a hard ground (low impedance - just a wire). Since the benches are on concrete they likely have a path to ground that way and that might be lower impedance than an ESD high impedance connection. I would do a high impedance ground on the benches and use an ESD mat.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,113
Location
NJ
For board work, i have always been around wooden topped benches. The frames were grounde. When needed, esd mats and wrist straps were used on top of the wood. Not too often however.

At home, I frequently use the steel top of my tablesaw with a large piece of cardboard beneath the work, especially when 120 or 240volt stuff is opened up and plugged in for troubleshooting and repair.
Resting forearms on a bare surface while working could surely light you up.

Regardless of the methods used, you always need to know if you are grounded or isolated.
 