Regarding adding outlets using metal conduit. If your pulling a separate ground wire, (not depending on the conduit for ground) do you still pigtail to the metal box, just like your were running Romex?
Just plain old 115 outlets. I'm told here that we can use the conduit as the ground but if a joint becomes unstable the ground is lost, so it's best to run a seperate wire.
Anywhere you have a device(recep, switch, etc) or a splice in the wires, you need to ground the box. If you pull straight through a box with no splices, you don't need to ground it.
Anywhere you have a device(recep, switch, etc) or a splice in the wires, you need to ground the box. If you pull straight through a box with no splices, you don't need to ground it.
I spose using splice in the wire is as good as any but,,, (wouldnt mind seeing where that is written) when the device is mounted in a cover it needs to be grounded to the box via a jumper, if the device is mounted to the box its not needed.