Had the power company install a meter/load center combo panel at my property recently. It has 4 breaker spaces below the 200 amp main breaker. I want to install a 30 amp RV outlet right next to the panel.
Im surprised the power company did not install the NEC required pair of grounding electrodes..... ask them if they are suppose to.... this install is not NEC compliant....
My major question is about grounding the panel. Since it is a combo meter/panel, I know the ground and neutral is bonded inside the panel. If I understand correctly, what I need to do is install a ground rod and connect the ground rod strap with copper wire into the neutral/ground bus of the panel in order for my trailer outlet to be properly grounded.
Just wanted to double check, so appreciate if anyone could verify.
Thanks
Not quite.
youre mixing up things here.
Grounding electrodes have nothing to do with the ground pin on an outlet. grounding electrodes are for shunting lightning, limiting voltage to earth and shunting high voltage when PoCo primary lines contact secondary lines.
The ground pin on the outlet is an equipment grounding conductor for establishing a low impedance fault current pathway.
Dont confuse the 2 as they serve different purposes.
Your RV outlet will function perfectly fine without a grounding electrode but i would not use the service until you install the grounding electrodes in case of lightning...
That's what I wasn't sure of, if the ground/neutral bonding in the box is a good enough ground as is.
The neutral bonding in the main service panel has nothing to do with grounding electrodes. The neutral bonding is for establishing a low impedance fault current pathway so breakers can trip when current energizes metallic pathways that should not be energized....
They did not install a ground rod. I know the neutral and ground busses must NOT be bonded on any subpanels after the first one, and requires a ground rod, but unsure on if a ground rod is overkill/not needed or if it would be harmful since the neutral and grounds are bonded. I've installed breakers/outlets before, but it was on existing panels that already had ground rods installed.
a grounding electrode is not overkill nor harmful to a neutral bond since they do not have anything to do with each other. The NEC actually requires 2 grounding electrodes, not just one....
The REC does the same thing where I live. You are responsible for the ground rods. Two ground rods at least six feet apart. You need at least a #6 wire. Some places require a #4, so you may just want to go that route. Make sure you don't put the rods where they will interfere with future trenching. I usually go out from the back of the pole unless the trench is there, in which case I put them in the trench
Actually, NEC minimum size for GEC is #8 but requires protection. #6 does not need protection and #4 would be overkill here....