Well-known member
This was posted on another forum.....outstanding video and should be watched by all..
Many people want to see things in black and white.. Grounded or un-grounded. In reality, its not yes or no... Its all a gradient.
My answer is ufta.. or was that Ufer?
Good info...
I'm looking at how hooking my my low impedance Ufer grounded garage interacts with the 25 ohm ground rod on my house. My take is that current is flowing to the UFER ground on the garage.
Basically an unintended ground path out to the garage.
\So is this guy saying that ground rods are not needed? Then why have three prong grounded outlets? If I have what this guy is saying correct, then if I have a piece of equipment that's running say an air compressor, and there's a short in the motor where as 120v is touching the the motor casing which is grounded, that voltage is going to my ground rod outside the shop. so if I walk near the ground rod i get electrocuted?
So is this guy saying that ground rods are not needed? Then why have three prong grounded outlets? If I have what this guy is saying correct, then if I have a piece of equipment that's running say an air compressor, and there's a short in the motor where as 120v is touching the the motor casing which is grounded, that voltage is going to my ground rod outside the shop. so if I walk near the ground rod i get electrocuted?
This is not even remotely what the guy is saying. In fact he is saying the opposite.So is this guy saying that ground rods are not needed? Then why have three prong grounded outlets? If I have what this guy is saying correct, then if I have a piece of equipment that's running say an air compressor, and there's a short in the motor where as 120v is touching the the motor casing which is grounded, that voltage is going to my ground rod outside the shop. so if I walk near the ground rod i get electrocuted?
It is interesting that almost no home small appliances have a ground connection. Same is true with hand held power tools.
The except desktop computers.
PERFECT quote.You have to love the pics...if you can't understand them....well, put down the screwdriver
With respect to the solar array not being grounded. People are going to be hard pressed to change that. There isn't a POCO, Insurance Company, Electrician, or Inspector that will allow a grid tied solar array NOT grounded to Earth ground.
I don't think Mike Holt was talking about no ground connection at all, he was talking about a separate ground connection...his graphic marked as 'wrong' showed the solar array connected to a ground rod but it was separate and not connected back to the main ground.

I don't think Mike Holt was talking about no ground connection at all, he was talking about a separate ground connection...his graphic marked as 'wrong' showed the solar array connected to a ground rod but it was separate and not connected back to the main ground.
This ^^^^
The array should be bonded to the main ground and not use a second ground rod, and if you do use a second ground rod it needs to be bonded to the main rod.
I hope you realize a (separate) chassis ground is always used in a grid tied solar array. It is not tied to the main ground, right or wrong.
Remember, in his illustration it is assumed that the lightning struck the ground and went up. He does not address the point that if the solar array on your roof got struck by lightning at the panels, that a chassis / component ground would divert that energy to the ground.
This is why everyone is all over the map. People can baffle you with bull ****, or back it up with 999999999999999 pages of test, charts, graphs.
What is a person to do?
Chassis grounds are tied to the "main ground", it's an EGC. Same with a roof-top AC unit's metal chassis or anything else. This is REQUIRED by the NEC and NOT OPTIONAL. As he said 10 times you cannot avoid grounding according to the NEC because the manual says you should, but you can add an additional ground rod tied to the EGC IF it requires it as that is not prohibited.
Remember - this is a video targeted towards electrical professionals, and it is their responsibility to install things according to manufacturer specs no matter right or wrong - the underlying message to that is, even if a generator or panel calls for a separate ground rod, it's not the best option. So if you're a homeowner it's better to do things right than according to the manual
He does address that, by saying you do not protect something from lightning by making it a part of the lightning protection, you protect around them. What this means is if you plan on protecting the panels from lightning, do so by placing lightning protection around the panels... not turning them into lightning rods themselves by making them the easiest path to ground.
If a solar array is directly struck by lightning, having the chassis grounded is very likely not going to save things. If a short in the inverter, or a lag bolt from the panels hit a live wire, or whatever energizes the panel chassis... that equipment ground being connected at the main panel will chances are clear the fault.
My guess is given houses typical proximities to trees, power poles, etc... the vast majority of household lightning damage is NOT from direct strikes. We had a lightning storm and lost a bunch of stuff as did several neighbors, and it was not a direct hit and randomly targeted things as lightning tends to do.
I think this video did a pretty good job of summing things up. The NEC, Mike Holt, etc. are all on the same page. If you're a homeowner do things correctly - if you're an electrical contractor, you're limited by what the equipment's installation information requires unless it's specifically addressed by the manufacturer.
If I was some Joe Smoe and didn't have anyone to look over or care about my install. I could very well follow everything Mike Holt advised.It is interesting that almost no home small appliances have a ground connection. Same is true with hand held power tools.
The except desktop computers.
To clarify even further, are you asking if it needs to be connected to a grounding electrode (ground rod)?So to clarify...
My portable 10k watt generator does not need to be grounded? Correct?
To clarify even further, are you asking if it needs to be connected to a grounding electrode (ground rod)?
If so, the answer is no.
The idea of the video is great. The execution of it is really poor.
Seems about 1/3 information, 1/3 rant, and 1/3 bragging/story telling. Could have been done so much better.
Lots of people saying that the grounding rod isn't very useful, but it's there for a reason. My understanding is that it's mostly used so that the POCO can ensure that it's neutral/return line is at the same potential as earth. Basically, every household serviced works together to offer a low resistance path to ground.
It's part of a larger series/panel, it probably made more sense in that context.
I'm not sure anyone said a grounding rod wasn't useful. The point was they're NOT useful and perhaps detrimental in a lot of additional applications.
The purpose of the ground rods are to dissipate lightning/static charges/etc. Didn't you learn anything?![]()
This is (almost) completely wrong.Basically, every household serviced works together to offer a low resistance path to ground.
Can one imagine what would happen if the metal plumbing in your house was not bonded to the ground.....and a live wire got nicked and touched said plumbing? Showers would be fun.
Can one imagine what would happen if the metal plumbing in your house was not bonded to the ground.....and a live wire got nicked and touched said plumbing? Showers would be fun.
Well, again, much of this is wrong.If you want to get a good understanding of grounding issues, look for the topic "ground loops" on digital design web sites or books. Mike mentions "electronics" several times and should say what he means by that instead of just giving the impression that it is things with circuit boards.
I would like this video MUCH better if Mike would say "separate grounds" instead of just "grounds". You want your equipment grounded, but only in one spot with only one wire to that spot. You don't want a generator to have a separate ground than the ground system in your house, doing so leads to the problems he is describing. You DO want your generator grounded, but with a nice big SINGLE wire that leads to the ground bond on your main panel; and if you can arrange it you want your generator insulated (rubber grommets in the cover mounting holes will work) from the concrete pad it sits on to prevent a separate ground connection from being formed. The same with the rest of the equipment he lists, you want it grounded through the main panel ground bond, NOT through a separate ground rod that would form an electrical loop with the main ground of your house. It's this ground loop, with your equipment in the middle of it that causes problems with lightning etc.
"More grounding" is not "better grounding"; "better grounding" is described as a single lower resistance path to ground. You want to drop that 25 ohm figure Mike keeps mentioning; and having separate ground rods distributed through your electrical system doesn't do that. Dropping a 20 foot section of 1" copper pipe alongside the foundation, then tying it to your main panel with insulated 0 gauge wire welded to the pipe instead of driving a six foot rod and using those bolt on clip connectors gives a better, i.e. lower resistance, ground; all of it buried deeply enough to eliminate the "step potential" problem that he also mentions.
Well, again, much of this is wrong.
Ground loops are not an issue in AC building wiring.
In electronics and sound systems withing the structure, yes, they can be an issue, but as far as the workings and safety of an ELECTRICAL system, NO.
Not to sound rude, but you seem like the typical EE that thinks these type of things have any bearing on building wiring.