sansert
Well-known member
Wondering what the grounding requirements are for installing a 60 amp sub panel in new garage?
Wondering what the grounding requirements are for installing a 60 amp sub panel in new garage?
Need more info.
Is this an attached or detached garage?
If attached, then you only need the EGC.
If detached, then you need grounding electrodes in addition to the EGC.
Yes this will be a detached garage. Wood frame.
My total run will be 70 feet from panel to panel.
So 2 grounding electrodes at least 6 ft apart? What size ground wire?
With this being in PVC pipe, would it be best to run burial cable or THWN for my sub panel feed.
I will have a PTAC heat/air conditioner which is 208V. No other really large loads.
What size feeder? That determines the grounding conductor size. A 208V PTAC cannot be used on a 240V supply you will need a buck/boost transformer to buck the voltage down. As to direct bury VS conduit, IMHO conduit is cheap insurance.
The PTAC is listed at 208/230V if that makes any difference in my previous question.
As far as the feed, I have been told #6 to the sub panel. 2 Hots, 1 neutral, and 1 ground
A single phase 208v ptec will run fine on 240v.What size feeder? That determines the grounding conductor size. A 208V PTAC cannot be used on a 240V supply you will need a buck/boost transformer to buck the voltage down. As to direct bury VS conduit, IMHO conduit is cheap insurance.
A single phase 208v ptec will run fine on 240v.
I do the same, have one today, 2 alum feeding a 24 space and going to put a 60 feeding it. The stores do have pre cut ground wire, they had 5, 15 ft 25 and 50. They had 15 ft of 8. I believe 8 is legal for 100A.HD stocks #6 bare copper ground in a package, along with the ground rods and clamps you need. I don't remember the length, but I think the wire is about 20-25 feet, which is usually enough to route from the panel, through the wall and make a continous connection to both rods.
As wyliediesels explained, your sub-panel may not have a separate grounding bar, so you need to add one so that you can separate grounds and neutral. HD also carries the ground bars for several panel brands. You also must remove the jumper in the panel so that ground and neutral are separate.
The distance to my garage is similar, and I ran 2" conduit with 2-2-2-4 AL MHF. Its a very common solution, and the wire I purchased is dual rated for both direct burial and inside use within conduit. You may only need to run wiring inside the building for a short distance, but using dual rated MHF and conduit makes it code-compliant. The MHF can be breakered for up to 90 amps in the main panel (I used a 60 instead), and I used a 24 space 100 amp sub-panel.
Bruce
how did you get the 2 wire to fit in the 60 amp breaker, mine wouldn’t come close to fitting.HD stocks #6 bare copper ground in a package, along with the ground rods and clamps you need. I don't remember the length, but I think the wire is about 20-25 feet, which is usually enough to route from the panel, through the wall and make a continous connection to both rods.
As wyliediesels explained, your sub-panel may not have a separate grounding bar, so you need to add one so that you can separate grounds and neutral. HD also carries the ground bars for several panel brands. You also must remove the jumper in the panel so that ground and neutral are separate.
The distance to my garage is similar, and I ran 2" conduit with 2-2-2-4 AL MHF. Its a very common solution, and the wire I purchased is dual rated for both direct burial and inside use within conduit. You may only need to run wiring inside the building for a short distance, but using dual rated MHF and conduit makes it code-compliant. The MHF can be breakered for up to 90 amps in the main panel (I used a 60 instead), and I used a 24 space 100 amp sub-panel.
Bruce
I do the same, have one today, 2 alum feeding a 24 space and going to put a 60 feeding it. The stores do have pre cut ground wire, they had 5, 15 ft 25 and 50. They had 15 ft of 8. I believe 8 is legal for 100A.
Since this is new construction, look into whether you should use an Ufer ground instead of ground rods.
Ask your AHJ first. In my city, either UFER or rods is OK. In the next town if you don't have BOTH you get red tagged. There's NEC and then there's local. Better to ask now than find out you missed something later. Inspectors don't do forgiveness LOL.
I'm using Square D QO panels on both ends, and IIRC the 2-2-2-4 AL fit into the panel connections and the 60 amp breaker without any problem. Maybe the Square D breakers have bigger connection points.
I did have to modify the new isolated grounding bar in the sub-panel by adding a larger lug for the 4 gauge ground in the 2-2-2-4.
Bruce
Why do you have an isolated ground bar?