If the OP puts in a 30a ckt in his new conduit network, he runs a #10 egc for it and then it’s required all throughout the remainder of that home-runned conduit network. This then includes any other 15a and 20a ckts in this same conduit network vs not having to pull any egc in the first place?
No
The #10 ground wire would be ended where the 30 Amp circuit terminates.
A #14 or #12 would be required from that point on for any 15 or 20 amp circuits respectively, and would be spliced to the #10.
Edit: An exception to this would be if the 15 or 20 amp circuits for some reason had run #10 wire to them.