Mr Trees has made nothing but good points. This one alone is a reason to not do the panel if you do not know what he is talking about.
In a nutshell: One white neutral wire can service 2 hot wires, one from each side of the panel On older homes, it can be harder to discern which hots and which neutral make a particular multiwire circuit.
Here is the panel problem: If you don't know which hots are multiwired to make a particular multiwire circuit, you can't have safe over-protection. Specifically, if neutral connection in a multiwire is broken, hot wires will carry 240 volts. For this reason, mutiwire hots have to be tied together so if one trips, the other does too.
I use double pole breakers when I run a multiwire circuit. Some jurisdictions allow mechanical ties between the breakers. If you trip one breaker to say, change an outlet, and the neutrals are not pig-tailed (and they won't be on an old house) you can send 240 volts down the other hot wire that isn't switched off.
If you can't accurately identify which (if any) wires are multiwired then you can't put them on a double pole breaker.
If you don't know what a 'multiwire' circuit is, I'd at least hire an electrician to label the old box and ID multiwire circuits before you start.
No you can't send 240 volts to equipment on a MWBC if one of the breakers is off and the other is on. You can get electrocuted working on the neutral as it is still carrying current from the other breaker.