Do some research on Ufer grounds.
Most jurisdictions are going to want at least a 20' long piece of #4 or #6 copper wire embedded in your foundation. In most cases, the rebar alone is not enough. And, the copper wire needs to be at the bottom of the footing.
You may want to take your own advice??
Ufer grounds are known in the NEC as "concrete encased electrodes"
From the 2011 NEC
(3) Concrete-Encased Electrode. A concrete-encased electrode shall consist of at least 6.0 m (20 ft) of either (1) or (2):
(1) One or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1⁄2 in.) in diameter, installed in one continuous 6.0 m (20 ft) length, or if in multiple
pieces connected together by the usual steel tie wires, exothermic welding, welding, or other effective means to create a 6.0 m (20 ft) or greater length; or
(2) Bare copper conductor not smaller than
4 AWG
An inspector must accept these, unless there is a local amendment.