grounding rod question

06manvan

Member
Joined
Aug 3, 2015
Messages
12
Getting my metal garage installed with rebar into the ground. Would that be considered a grounding rod or no?
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The primary grounding electrode is now the footer steel and there needs to be a place to connect it. My footer steel is bonded to the building, a whole array of it sits basically in water with water behind it a bit in a loading dock and for some reason when I built I pounded a rod thru it, acorn under the footer, 8 ft of standing water. The whole place is a giant uffer plus the 2 aux rods and in some sense 300 ft of steel pipe casing.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I remember a couple lights coming on when I had a problem with a well. I asked the well guy about proper grounding for the service and he didn't know squat. I quiz a couple eld timers on a forum I know they know and the guy says bug it to the steel casing and I say welding a lug to it work, you bet. For that only 1 electrode and no rods needed or wanted.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,725
Location
SE Michigan
Leave one bar approx. 1-2 feet proud of the footing/stem wall top for use later. In my opinion it needs to be encased in a concrete wall or pad footing or thickened edge/grade beam that bears directly on the soil for it to work, and not a rebar grid in a simple flat slab that's supported by a vapor barrier and then a crushed gravel pad. The action of the concrete against the soil multiplied by all of the surface area is what enables it to work. Google Ufer Ground for more info and code references.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Do some research on Ufer grounds.

Most jurisdictions are going to want at least a 20' long piece of #4 or #6 copper wire embedded in your foundation. In most cases, the rebar alone is not enough. And, the copper wire needs to be at the bottom of the footing.

But nothing wrong with also tying the copper wire to your rebar.

Me? I have the copper wire....tied to my rebar....tied to my existing ground rods and copper plumbing.

You can never have enough grounding....
 
OP
0

06manvan

Member
Joined
Aug 3, 2015
Messages
12
For clarification there will be no concrete floor, just crushed conpacted floor
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Do some research on Ufer grounds.

Most jurisdictions are going to want at least a 20' long piece of #4 or #6 copper wire embedded in your foundation. In most cases, the rebar alone is not enough. And, the copper wire needs to be at the bottom of the footing.

You may want to take your own advice??

Ufer grounds are known in the NEC as "concrete encased electrodes"

From the 2011 NEC

(3) Concrete-Encased Electrode. A concrete-encased electrode shall consist of at least 6.0 m (20 ft) of either (1) or (2):

(1) One or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1⁄2 in.) in diameter, installed in one continuous 6.0 m (20 ft) length, or if in multiple
pieces connected together by the usual steel tie wires, exothermic welding, welding, or other effective means to create a 6.0 m (20 ft) or greater length; or

(2) Bare copper conductor not smaller than 4 AWG


An inspector must accept these, unless there is a local amendment.
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
06manvan

A rebar in the dirt is insufficient.
You need genuine ground rods - 2 of them (unless you can prove that 1 provides less than 25 ohms to ground)

They need to be buried to a depth of 8', and be more than 6' apart.

They need to be connected to the ground bar in the panel with a #6.
 
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I used the 20' of #4 in my slab, no problem with inspection. BUT - only because I'm here and not 20 miles down the road, where they require both a UFER and the copper line or driven rods. The why could be debated, only talking to local contractors, architects, home builders, etc - you get a universal answer to the "permits and inspections" question of "Don't get me started.' :)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
A stick of rebar pounded into the dirt would NOT qualify as a grounding electrode. Buy 2 8' rods, acorn clamps and some bare solid #6 cu wire and be done with it.

How is the garage being fed? From a house or its own service?
 

MushCreek

Well-known member
Joined
Jan 14, 2015
Messages
9,763
Location
Upstate South Carolina
I just installed two 8' ground rods, which is what they usually require here. The inspector told me I only needed one because it is a sub-panel from the house. Huh? Either way, the second ground rod can't hurt, and after pounding on it for an hour, I'm going to use it!
 