Detached new garage build with 60 amp subpanel from main house. Used UF 6/3 all the way. Neutral and equipment ground at the subpanel. Most of the threads discuss putting two grounding rods at the garage but we were told it wasn't necessary with this set up and since the house is already grounded. True or false? If it is necessary, how would we add those?
Make sure that the neutral bus is isolated in the subpanel. U may need a seperate ground bar kit.
If lightning hits your detached structure and there is no rods there, then the lightning has no where to go but down the wires that connect to your house.
EVERY detached structure requires grounding electrodes regardless of what the feeding structure has.
U add 2 rods by connecting them with one continous piece of #6 bare solid cu wire (or u can use #8 cu but that requires conduit) making sure its not subject to damage and connecting it to the ground bar in the subpanel.
l,
The only person who can correctly answer the question for you is the person who will be doing the final inspection.
Actually the NEC already answers it. The inspector should just be saying what the NEC calls for.
This is rural and won't be inspected but we want it to be safe. Too late for a UFER, the garage is finished. Are one or two grounding rods needed for safety? And if so, could someone please explain why the house grounding is insufficient. Thanks so much.
Explained above.
My electrical utility only requires one ground rod for house service. I installed 2 anyway at the service entrance.
I installed an additional 1 rod per subpanel. Electrical utility didn't require it but it made me feel good.
Doesnt matter what the PoCo requires. They arent the authority that regulates inside wiring. The NEC requires 2 if 25 ohms or less of resistance to ground cant be proven.
Ground, dirt, rocks etc. has resistance. It's the same reason for shuffling with your feet close together if you find yourself near a downed power line. Basically you are keeping both feet at the same potential. get them too far apart and your legs could be the path of least resistance.
If there is less than 25 Ohms resistance between the buildings then they will be close enough to the same potential that the separate ground is not required.
Ohms law I=V/R.
The NEC still requires grounding electrodes regardless of the potential between buildings.