Finally getting to the point of (almost) ready to hook up electrical on my new detached shop. I have 4 wire running from the disconnect at the meter to my panel in the building. I understand the earth ground goes to the the Ufer or ground rod, but should it also be bonded to the steel framing of the building? The building is a weld up steel frame with metal siding.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You want the earth you ae standing on, any steel, all the machines in the whole place all connected to the 4th wire. Eliminate any potential difference between it all and a low impedance pathway for any fault back to the neutral main.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
What would be the proper way to do that?

Bolt a lug to the steel and 8 for 100 or 6 to 200,, to the steel and to the ground bar. Bolt it somewhere it's visable. I use 6 anyway. I described it in another thread, just did one I bonded with a lug on the way to the rods. Use a bolt or threaded connection and not a self driller as I recall.
 
Last edited:

tonyprovo723

Well-known member
Joined
Jul 2, 2016
Messages
150
For residential it may not matter, but thought I heard a #6 grd wire does not need to be in conduit while anything smaller does need to be in a protective raceway. This would explain why #6 is more common in commercial applications as a minimum size.(My observation for what is worth.)

Sent from my SM-G965U using The Garage Journal mobile app
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Ideally it should be the same or better than the 4th wire. I think on some service entrance (different than 4 wire) it should be a size larger.
 

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
For residential it may not matter, but thought I heard a #6 grd wire does not need to be in conduit while anything smaller does need to be in a protective raceway. This would explain why #6 is more common in commercial applications as a minimum size.(My observation for what is worth.)

Sent from my SM-G965U using The Garage Journal mobile app

Same in residential.
 