Grounding

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,881
Location
AK
Between a remote mounted meter panel and the main breaker panel, does there need to be a dedicated ground?
IE 4 wires?

As far as I knew that was the case, but I think they just have a ground rod at each location. Which I guess "in theory" would do the same thing.

I can't trust any of the wiring. Tripped on the ground wire for the gas meter a few days ago. Ton of rain had washed away a bit of gravel.
They took a couple foot length of rebar, wrapped the ground wire 5-6 times around the end, flat the rebar flat and put gravel over it.
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Between a remote mounted meter panel

This has a breaker or disconnect?

Then yes, the feed to the next panel needs 4 wires per current NEC*

*I have no clue what cycle Alaska is currently on, and if this was done before the "new" code was adopted then it's technically ok to have 3 wire.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,627
Location
BC
Conversely, if this is just a meter base (no breakers or disconnect), then no.

But watch out for the Utility's demands. Sometimes they overrule and say they won't allow a substantially long unprotected feeder, so they enforce a disconnect, and you need 4-wire.
 

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,350
Location
Hunterdon County NJ
But watch out for the Utility's demands. Sometimes they overrule and say they won't allow a substantially long unprotected feeder, so they enforce a disconnect, and you need 4-wire.
^ TRUE!…….. MEET with the utility company rep because they have their own set of rules.

BTW! Some utilities don’t allow a "driven ground" wire in their metering sockets.
 

chinboys

Well-known member
Joined
Jun 20, 2011
Messages
434
You can never have enough grounding but the question is really whether the respective "boxes" are themselves bonded to the utility's neutral line.
From the description, it appears you have a main panel and subpanel for the boxes.
NEC codes dictate the main panel be bonded and the subpanel not be bonded.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,143
Location
Modesto, CA
Between a remote mounted meter panel and the main breaker panel, does there need to be a dedicated ground? IE 4 wires?

As far as I knew that was the case, but I think they just have a ground rod at each location. Which I guess "in theory" would do the same thing.
Is there a disconnect at the meter?

The EGC (between panels) and grounding electrodes are most definitely not the same animal.

go read the write up here on my FAQ, regarding EGCs and grounding electrodes.


Also read post #3 on the same FAQ. it explains 3-wire vs 4-wire
I can't trust any of the wiring. Tripped on the ground wire for the gas meter a few days ago. Ton of rain had washed away a bit of gravel.
They took a couple foot length of rebar, wrapped the ground wire 5-6 times around the end, flat the rebar flat and put gravel over it.
yeah thats not kosher
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,143
Location
Modesto, CA
But watch out for the Utility's demands. Sometimes they overrule and say they won't allow a substantially long unprotected feeder, so they enforce a disconnect, and you need 4-wire.
umm unless the PoCo is also the AHJ, the PoCos responsibility and authority stops at the meter. what utility has a mandate of no "substantially long unprotected feeder"? whatever that means (no defined length?)....
 
To avoid these ads, REGISTER NOW!

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,340
Location
West central Indiana
Between a remote mounted meter panel and the main breaker panel, does there need to be a dedicated ground?
IE 4 wires?

As far as I knew that was the case, but I think they just have a ground rod at each location. Which I guess "in theory" would do the same thing.

I can't trust any of the wiring. Tripped on the ground wire for the gas meter a few days ago. Ton of rain had washed away a bit of gravel.
They took a couple foot length of rebar, wrapped the ground wire 5-6 times around the end, flat the rebar flat and put gravel over it.
Are you sure it’s a ground wire?

With yellow poly gas pipe they bury a tracer wire for line location in the future. Underground piping isn’t grounded by code and more recent versions actually require electrical isolation via a dielectric union from the houses piping which of course is not needed with poly pipe just copper.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
he could be referring to the main breaker in the panel in the building.
He could be referring to the breaker in my house.

But in context it seems clear that he was referring to the breaker in the meter pedestal that he was posting about, after at least 2 of us asked if it was just a meter or if it included a breaker.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,627
Location
BC
umm unless the PoCo is also the AHJ, the PoCos responsibility and authority stops at the meter. what utility has a mandate of no "substantially long unprotected feeder"? whatever that means (no defined length?)....
When they decide its too long, they refuse to hook up power, and insist on a disconnect @ meter. The have full authority to make demands that exceed Code. Pretty simple.
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,881
Location
AK
Are you sure it’s a ground wire?

With yellow poly gas pipe they bury a tracer wire for line location in the future. Underground piping isn’t grounded by code and more recent versions actually require electrical isolation via a dielectric union from the houses piping which of course is not needed with poly pipe just copper.
Yes, it's clamped to the steel gas piping.
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,881
Location
AK
He could be referring to the breaker in my house.

But in context it seems clear that he was referring to the breaker in the meter pedestal that he was posting about, after at least 2 of us asked if it was just a meter or if it included a breaker.
Yes. Meter panel has 100 amp main breaker.
Panel in building is breakers for all the branch circuits.
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,881
Location
AK
Wow, even the gas company guys in alaska are really messed up
I'm not sure who grounded it.

I know at my old place the water line was grounded in the same ground for the house panel.
The meter panel if that place was in the house.

This place it's just in a plywood and 2x6 in the middle of the yard, more or less in between the shop and house pad.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,143
Location
Modesto, CA
When they decide its too long, they refuse to hook up power, and insist on a disconnect @ meter. The have full authority to make demands that exceed Code. Pretty simple.
wrong at least here. PoCo is not the AHJ and has no such authority. maybe your PoCo is different but your blanket statement does not cover all regions. Also PoCos do not have to abide by NEC code and most of them have no clue whats even in the NEC. They go by different rules that stop at the meter socket
 