A Mike Holt paper on the use of handle ties on single pole breakers.
Click here for a PDF download.
Charles
Click here for a PDF download.
Charles
Is there ever an advantage to using them? I do not care about cost or availability for my own work, as I have all of the correct items needed before the job starts. It does drive me nuts that my main in 4 breakers tied together, vs the Square D QO main style.
Ryan
It is very well put, but I'll be damned if I'll ever use a handle tie.
The fact that in the event of an overload, the breakers can independently trip just seems idiotic to me. I'll stick with internally linked 2-pole breakers for this usage.
Everybody's an electrician. The NEC allows handle tied breakers under certain circumstances, and if you follow the rules there shouldn't be any issues.
On a MWBC handle tied breakers are fine. The code requirement is only that the disconnect (in this case the breakers) has to turn off all circuits with a common neutral.
The reason is that if the neutral became disconnected while repairs were being done, and one circuit was still hot, the neutral would become a hot wire.