I've perused other threads regarding hanging garage heaters but haven't seen any hard data on strength of lag bolts in wood.

I just hung a 45K BTU Beacon-Morris heater in my new 28ft x 30ft detached garage using 2-1/2in long, 5/16in lag bolts. See pics. The Unistrut is suspending under the 2x8 joists at 5 points.

The heater only weighs 65lbs, so each of the lag bolts only holds up approx. 13lbs, not counting the weight of the unistrut, the stack, and plumbing etc.

I found myself lying in bed last night wondering if the 5/16in lag bolts are sufficiently strong enough considering the wind loading on the stack, walking around in the attic above the heater, wood contraction and expansion, building wracking, etc.

It's easy enough to change out the 5/16in lag bolts for 3/8in or even something bigger, but I imagine there is a point of diminishing returns.

Am I just being paranoid?


Locating heater with a drywall lift from suggestion on Garage Journal!
attachment.php


Hanging from unistrut lagged bolted in to the joists with 5/16" by 2-1/2" long lag bolts.
attachment.php
 

Attachments

  • Garage_Heater_on_Drywall_Lift.jpg
    Garage_Heater_on_Drywall_Lift.jpg
    147.5 KB · Views: 462
  • Garage_Heater_Hang_cropped.jpg
    Garage_Heater_Hang_cropped.jpg
    132.9 KB · Views: 466
Last edited:
To avoid these ads, REGISTER NOW!

Rockhead261

Well-known member
Joined
Aug 28, 2013
Messages
1,911
Location
10509
Why didn't you place the strut on TOP of the joists and hang the unit with longer rod?

Sent from my SCH-I545 using Tapatalk
 
OP
J

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,820
Location
Southeast Michigan
Why didn't you place the strut on TOP of the joists and hang the unit with longer rod?

Sent from my SCH-I545 using Tapatalk

For optimal placement of the heater, considering the stack and the gas line, the floor above gets in the way of placing the unistrut above the joists.
 
To avoid these ads, REGISTER NOW!

gregtwojeeps

Well-known member
Joined
Jul 30, 2013
Messages
5,096
Location
Ky
Should be fine. Anytime I mount supports to a ceiling/wall for an apparatus I always put my "engineered" load test on it :) . I grab it and just hang on it. If it supports my 210 pounds, it will hold anything up to a 100 pounds.
 

PugetDude

ALLIANCE MEMBER
Joined
Mar 13, 2013
Messages
22,461
Location
Superstition Mountains, AZ
There's a diminishing return, because it is still limited by the tensile strength of the fastener, but yeah, you have nothing to worry about.

Ultimate tensile strength of a lag bolt is generally calculated with a thread penetration of 10 to 12 times the bolt diameter in softwood species.

So, in typical framing lumber, you'd be looking at about 3"-3.75" penetration with an ultimate tensile strength of 600-740 LB per bolt- 2400#-2960# for a 4-bolt connection. With a 65 # heater you're looking at a safety factor of 37x-45X; you should be plenty safe.
 

BD1

Well-known member
Joined
Mar 18, 2007
Messages
4,602
Location
north side
IF, you didn't want the unistrut on top of joists as mentioned, I would have thru bolted angle clips to joists and bolt unistrut to them or drop rods down to the unistrut depend on angle clip dimensions.
 