Background:
Went home, house was hot, Thermostat was on cool, Air Handler was blowing warm air. I checked the coolant lines, they weren't cold. Went outside and checked the heat pump, it was dead.
Pulled the cover, the LED monitor referred me to an "open circuit". I checked the capacitor, it appeared slightly bulged and oily. I tested it with my multimeter and it was dead.
I replaced it. Turned the system back on and voila..........cool air.
Now onto the problem:
The units will not shutdown when they have reached the setting on the thermostat. If I bump the temperature up on the thermostat the relay kicks and the system shuts off, if I don't touch it, the whole system just keeps running.
I am guessing that it why the capacitor went bad? I thought it was the thermostat, so I placed it on my other unit, it works fine.
Any ideas on what could be causing it to stay on?
Went home, house was hot, Thermostat was on cool, Air Handler was blowing warm air. I checked the coolant lines, they weren't cold. Went outside and checked the heat pump, it was dead.
Pulled the cover, the LED monitor referred me to an "open circuit". I checked the capacitor, it appeared slightly bulged and oily. I tested it with my multimeter and it was dead.
I replaced it. Turned the system back on and voila..........cool air.
Now onto the problem:
The units will not shutdown when they have reached the setting on the thermostat. If I bump the temperature up on the thermostat the relay kicks and the system shuts off, if I don't touch it, the whole system just keeps running.
I am guessing that it why the capacitor went bad? I thought it was the thermostat, so I placed it on my other unit, it works fine.
Any ideas on what could be causing it to stay on?
Last edited: