I just received my Sterling GG 120k BTU propane heater for the shop and came across NFPA specs on combustion air intake area requirements that contradict the manufacturer specs.
The manual states the NFPA requires 1 square inch of intake area for every 5,000 BTU input rating of appliances. At 120,000 BTU input rating for my heater, it would require a 24 square inch intake area. The manual also specs a 5" heater intake pipe, but that's only 19.63 square inches.
Is the heater input derated for some reason that allows the use of a smaller area intake or is it the use of a blower or ???
Not that it makes a difference to me, I'm still installing it per the manual. I'm just curious.
The manual states the NFPA requires 1 square inch of intake area for every 5,000 BTU input rating of appliances. At 120,000 BTU input rating for my heater, it would require a 24 square inch intake area. The manual also specs a 5" heater intake pipe, but that's only 19.63 square inches.
Is the heater input derated for some reason that allows the use of a smaller area intake or is it the use of a blower or ???
Not that it makes a difference to me, I'm still installing it per the manual. I'm just curious.