I recently installed a 40k BTU radiant tube heater with a Honeywell smart valve in my garage. It's been fairly cold around these parts (-35) and I noticed the heater is not keeping up. After doing some investigating, I noticed that the heater is only running at 24k BTU. I had a friend with a gas meter test the pressure, and it has good pressure coming to the heater, but after the valve it has next to no pressure.

Does anyone know what the cause might be? The plumber said they installed the correct conversion kit to NG as it used to be a LP heater. I don't really want to get the plumber back if I don't have to as he already bent me over on the install bill.
 
Last edited:
To avoid these ads, REGISTER NOW!

sms1974

Well-known member
Joined
Jul 9, 2014
Messages
210
Location
Grafton Ohio
You need to get some one able to adjust the output pressure on the gas valve. Its an easy job for a heating tech. most likely the pressure is low which will give you the lower btu output.
 
OP
C

corner27

Member
Joined
Oct 4, 2009
Messages
22
My friend that tested the pressure did adjust it a bit, but he didnt want to screw the adjustment too far because he said there is no stop and the screw will go all the way into the manifold.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
In order to get the correct pressure at the manifold you'll. Need to use a manometer .
Is the guy sure he put the nat gas burner office in ? Getting 1/2 of your rating makes me wonder ?
You'll also have issues with to small a gas line , distance etc.
 
Last edited:
OP
C

corner27

Member
Joined
Oct 4, 2009
Messages
22
The plumber ran the line and installed the conversion kit. He told me that he put the correct kit in, but I'll double check with him on monday.
My friend tested the pressure with a manometer. That is how we narrowed the problem down to after the valve.
 
To avoid these ads, REGISTER NOW!

slice

Well-known member
Joined
Jun 16, 2010
Messages
331
Plumber did not set it properly. It's on him to do the job correctly.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
How old was the unit when you got it? It could be an install issue or maybe the valve is just going south,time to open it up and check the kit that was installed in there.;)
 
OP
C

corner27

Member
Joined
Oct 4, 2009
Messages
22
How old was the unit when you got it? It could be an install issue or maybe the valve is just going south,time to open it up and check the kit that was installed in there.;)

The unit was bought second hand, but was never installed. The PO bought it with intentions of installing it in his garage, but ended up selling his house, so he sold the heater.
 