I finally got this compressor running (1960s Saylor beall 705) to make sure everything works before I rebuild and paint. Temp. power to the control box #10 wire on a 40 amp breaker. The compressor started and this thing is smooth running...it pump to about 100psi and the contacts in this control box arced. Did I do something wrong???Or is something just worn out??? I dont understand how this electrical in this control box works. Can someone explain Please. What do I need???
 

Attachments

  • 20181208_171538.jpg
    20181208_171538.jpg
    96.4 KB · Views: 143
To avoid these ads, REGISTER NOW!

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,004
Location
Eastern North Carolina
Likely time for new replaceable contact points or a new motor starter, whichever is less expensive. Look it up by the numbers on the starter enclosure. They are easy to change, so it will boil down to expense. Contacts for some older units can be expensive or obsolete. Post the numbers for more help. There may be both a size and bulletin number.
 
Last edited:
OP
J

jamurr65

Member
Joined
Oct 28, 2018
Messages
18
Location
central square ny
RJ Where would the starter be located inside the motor??? because their is nothing on the outside of this motor nor has their ever been.
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,004
Location
Eastern North Carolina
RJ Where would the starter be located inside the motor??? because their is nothing on the outside of this motor nor has their ever been.

The box you pictured IS the motor starter. It is electrically activated to slam shut on startup and provide power to the motor. When the pressure switch is satisfied, it tells the starter to release and shut the motor off.
 
To avoid these ads, REGISTER NOW!

md21722

Well-known member
Joined
Nov 30, 2015
Messages
1,840
Location
Mt Juliet, TN

seber

Well-known member
Joined
May 31, 2016
Messages
4,195
Location
Deep East Tx.
Filing down the burned points to make them smooth is often a permanent fix. It will depend on how badly they have been allowed to get.
 
OP
J

jamurr65

Member
Joined
Oct 28, 2018
Messages
18
Location
central square ny
Here is a couple pictures of the starter, The red tag is from the base near what I think is a coil, it shows 30 amp max load. Does that mean I shouldn't have had this on a 40 amp breaker?? The contacts are pretty fried. Theirs another number on the coil. Also a pic of the overload protection, no idea what the dial is for, seems to be set on 100 ???
 

Attachments

  • 20181209_110706.jpg
    20181209_110706.jpg
    77.1 KB · Views: 26
  • 20181209_110621.jpg
    20181209_110621.jpg
    72.9 KB · Views: 25
  • 20181209_111127.jpg
    20181209_111127.jpg
    71.2 KB · Views: 27

Slupie

Well-known member
Joined
Dec 19, 2010
Messages
162
Location
Bartlett, IL
Here is a couple pictures of the starter, The red tag is from the base near what I think is a coil, it shows 30 amp max load. Does that mean I shouldn't have had this on a 40 amp breaker?? The contacts are pretty fried. Theirs another number on the coil. Also a pic of the overload protection, no idea what the dial is for, seems to be set on 100 ???

Here is some good info on GE Contactors and Overloads,
https://www.geindustrial.com/catalog/controlcatalog/01_CC.pdf

http://www.mag-trol.com/product-publications

Somewhere on your contactor it should say the model number and NEMA size. You have 208/220 VAC coil and GE CR124 overlaod. From the pictures I can't tell what NEMA size the contactor is and what size the overlaod heaters you have.

GE Overlaod heaters chart http://www.mag-trol.com/docs/tables/GE/ge-overload-relay-heater-table.pdf

You can buy a new motor contactor and overload from here https://www.automationdirect.com/ad...ols/iec_contactors_-z-_starters_-z-_overloads

You will need the motor voltage, amperage, HP and how it's used. Air compressor starter wiring is slightly different than push button start/stop on a table saw. If you are not sure give them a call and the'll help you make some choices.

It cost me $36 to buy a new one for my 1986 PM66 Table saw about 3 years ago.
 
Last edited:

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,004
Location
Eastern North Carolina
By the time you get through finding and paying for replacement contacts for this unit, you may be better off purchasing the starter in post #14. Contacts are likely to be $60+. If the starter is an obsolete model, more than that. I have had to change out older starters at work because of this. Trying to repair them was false economy.
 