Hi everyone, hoping someone on here can help me ID this wire that I have. Originally I was going to use it for wiring in a barn but sold the farm. I'd like to sell the wire vs scrapping it since it's good stuff, but will go that route if it's not easy to sell. It has 8 solid wires: 14ga x 6 wires, 12ga x 2 wires (white). I have close to 300 ft of it. I thought it was 3 phase but IIRC someone told me it wasn't.

Thanks in advance for the help.

IMG-5611.jpg
 
To avoid these ads, REGISTER NOW!

eejack

Well-known member
Joined
May 18, 2021
Messages
166
Location
the garden state
My guess is cubicle connections… its got conductors for 1 MWBC on 3 phase 208Y/120 and an additional set of conductors for a single circuit, giving the quad cubicle set 1 circuit per desk…
And....this thread is the answer.

 
To avoid these ads, REGISTER NOW!

eejack

Well-known member
Joined
May 18, 2021
Messages
166
Location
the garden state
Why the up sized neutral?
Non linear harmonics. Electronics ( specifically the then new electronic ballasts ) caused something of an issue. Oversizing neutrals were thought to eliminate or mitigate the additional loads on the neutral. I cannot claim to truly understand the issue, but I do recall all of the hubbub about it.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,252
Location
Coastal NJ
Non linear harmonics. Electronics ( specifically the then new electronic ballasts ) caused something of an issue. Oversizing neutrals were thought to eliminate or mitigate the additional loads on the neutral. I cannot claim to truly understand the issue, but I do recall all of the hubbub about it.
Supposedly some fires started in cubicle wiring from the overloaded neutrals. Odd harmonics add in magnitude leading to increased current in the neutrals.
 