Help interpreting Load Calc vs. MiniSplit Specs

Angelfire

Well-known member
Joined
Mar 22, 2012
Messages
1,367
Location
New Mexico and Ireland
Hiya Folks,
I had a load calc of my detached garage done a few years ago. Then got sent overseas for work and have now returned. My thoughts have turned back to getting this garage done so am dusting off the work I had done before. Anyway, ecomfort did a load calc on the space. I'll try to post a screenshot of what they provided. Ultimately, they indicated a 24k minisplit HP would suffice based on my area and the specs I provided them. This would be a 2 zone system with a 9k unit in one side of the garage and an 18k unit in the other (spec'ed out a 15k but those didn't seem to be available in the product line they were recommending). Anyway, I'm trying now to align their load calc with a different unit (everything they recommended was discontinued since the load calc was done) and am looking closer at cold weather performance which is where my knowledge of HVAC calculations is lacking. I'm in NM (Albuquerque) and while the winter temps aren't drastically cold, we do get the odd cold weather that drops into the single digits. While it is not essential to keep things toasty warm during this period, I am curious as to what I can expect from the units I'm looking at and here's where I'm asking for a little help. Attached is a chart showing the heating performance of a unit I'm considering and I'm really not sure how to read this and correlate it to the load calc. In the chart from the manufacturer, it indicates at an outside temperature of -4F and at an ambient of 70f indoors (DB), the btuh rating that is given is 15660. What confuses me about this is if the indoor temperature is higher, they indicate a smaller btuh number (ie. at 80F, the number has dropped to 15070 btuh). I had assumed this value was the value that the unit could produce at this outside temperature but given the input power is increasing as indoor temp rises, I am believing that the unit is working harder to meet the higher temps and hence it's overall output drops off a bit as the interior temp rises (probably a bad hypothesis by the way!). Also, I realize the load calc that was done was done for an outdoor temp of 18F....is there a way to step it back to say zero F and put a number on the btuh that is needed? I could do my own load calc on the building but was hoping there might be a simpler way of going about this.

Basically asking for any help to decipher what I'm looking at and whether or not this unit will keep the building somewhat warm at the lower temps. If it's easier, I'd be happy to send the full files via email or the like.

Thanking you experts in advance!
Cheers.
 

Attachments

  • Heat Calc.jpg
    Heat Calc.jpg
    126.8 KB · Views: 19
  • Gree Perf Chart.jpg
    Gree Perf Chart.jpg
    158.9 KB · Views: 21
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,429
Location
N CA
First off, I think you are overthinking this. For comparison I would suggest that you go to Fujitsu's site and run their heat loss calc. Manual J sizing has an 18% adder to the total heat loss for duct losses. As there are no ducts Fujitsu backs that factor out. If the output at the -4* meets your needs,then go for it. Understand that if that -4 is design temperature you will actually be at design temp less than .005% of the heating hours. Is it really a big deal if it gets 10* or so cooler in the space during that time. One thing. I was having a discussion with an LG mini-split distributor this week and he was telling me they are looking for a new vendor due to what they consider as a lack of warranty and tech support. Apparently they lost a lot of equipment in cold weather operation due to a lack of heaters in the condensing units. The base pan heaters are an option which no one was aware of. The better lines of minis have the base pan heaters built into their low temp units. Whatever you do, once installed stay on top of keeping the fans and coils clean to keep up the efficient operation of the system.
 
OP
A

Angelfire

Well-known member
Joined
Mar 22, 2012
Messages
1,367
Location
New Mexico and Ireland
Thanks Jack. Appreciate the input. I did a quick look at Fujitsu's site but came up empty with regards to their calculation. If you have it linked, could you post here?

Really though, my question is more general in terms of trying to understand the numbers. Attached in my initial post was the heat calc. done by ecomfort.com. This was based on an outside temp of 18F. What I'm trying to determine is what does this calc look like at say 5F and is there a way to scale down from 18F to determine what sort of BTUH I need at the lower temp.

Cheers.
 